Regarding the DC disconnect, the 2008 Handbook 690.14C(1) comments, "These 
requirements generally prohibit long runs of PV source and input circuits 
inside a building before reaching the required PV disconnect. A short conductor 
run through a wall at the point of first penetration to reach a disconnect 
mounted inside the building is allowed." I think an inspector could bump a long 
DC circuit through a building even if it was in conduit. What do you all think?

Joel Davidson
  ----- Original Message ----- 
  From: Bill Brooks 
  To: 'RE-wrenches' 
  Sent: Friday, December 18, 2009 8:32 PM
  Subject: Re: [RE-wrenches] 690.31E (through a building)


  Mark,

   

  The readily accessible disconnect at the inverter is all that is necessary 
according to the code. There may be practical reasons for additional 
disconnects, but if the system has no combiner box, or the combiner is at the 
inverter, only the disconnect at the inverter is required.

   

  Bill.

   

  From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Dickson
  Sent: Friday, December 18, 2009 3:25 PM
  To: 'RE-wrenches'
  Subject: [RE-wrenches] 690.31E (through a building)

   

  Hello there, 

  Due to a lot of concrete and asphalt, we are forced to run our PV source 
circuits in through one exterior wall, through a crawl space and out through 
the opposite exterior wall to our inverter and disconnect.  We will be using 
EMT and will not be making any stops while inside the building.  We will 
however need to place a couple of pull-boxes due the various required bends in 
excess of 360*.  Will we be required to place a DC disconnect at the "first 
readily accessible" point inside the building?

   

  Best regards,

   

  Mark Dickson,

  NABCEP Certified Solar PV Installer T

  Oasis Montana Inc.

   

   



------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to