I really studied this at one time, and what's interesting is that if a battery 
bank is too large, (regular discharges less than 20%) you're not really getting 
your money's worth, as the # of cycles x amount of discharge is less.  
Likewise, a battery that is discharged regularly deeper than 70% starts eating 
life too. It's surprisingly even however, from 20% DOD to around 70%; more 
cycles less discharge, or less cycles, more discharge, you get about the same 
total KWH total out of the pack over its life either way. (just take a cycle 
life chart for most batteries, and start multiplying cycles by DOD at different 
points)
The bottom line is, you might save some money upfront with a smaller battery 
bank, but it won't last as long. Therefore, the replacement cost ( labor to 
move out old bats, move in new) is higher with a smaller bank, so the total 
operating cost over the system life is higher, too.
Also, the charge rates that battery companies list are really for big, dumb 
on-grid chargers, not the 3 stage PWM units with temp comp that we use. I've 
found systems with really low charge rates to actually last a very long time. 
We're trading possible under charging and sulfation to avoid chronic over 
charging (and over heating) which is the real killer IMHO. Somewhere between is 
optimum.

I still do 5 days storage to 100% DOD, (or 4 days to 80%, same thing) for our 
avg. off grid systems, and tweak it down if we need to save money. Big systems 
with a good generator can work fine at less than 3 days. Of course local 
weather is a factor in this too. We get long spells of cold, cloudy weather 
followed by a couple of weeks of nice sun.

For GT w/ backup, I size for more like 8 hours. As was said before, they'll 
probably die from the float service, not the cycling. Even a really small 
battery will still work if the grid is out for a longer time, they'll just have 
to do more when the sun is out, and go to bed early.

R. Walters
r...@solarray.com
Solar Engineer




On Dec 1, 2009, at 3:15 PM, Travis Creswell wrote:

> IMHO, one of the worst design boo-boo’s is going past more then 2 days of 
> autonomy.  Personally, I no longer size much over one day because it’s my 
> anecdotal observation that most batteries die of old age and being ignored 
> long before cycles get them.  Speaking mostly about quality deep cycle 
> flooded.
>  
> Lots of good things result;
> -50%-75% smaller battery bank means a $20,000 battery bank just turned into 
> $5,000 bank which frees up a ton of money for more modules and now-a-days you 
> can buy a lot more PV with that money.  More array mean far less reliance on 
> autonomy.  I’ll take the trade all year long.  In the summer we have 3 to 4 
> weeks of sun and one day of clouds and in the winter we get 3 to 4 week 
> stretches with 1 sunny day.  Autonomy doesn’t really matter in either case 
> from what I’ve seen.  The larger the bank means more self discharge losses, 
> which on large battery banks gets significant as they age.  5-15 years later 
> you’ll still have all that array but no matter what you’re looking at new 
> battery bank.
>  
> -If you study the quality deep cycle manufacturers literature you’ll see that 
> you’ll see that anything over 1 day of autonomy is too much to allow the 
> array to actually charge the battery bank anywhere near the recommended amps 
> and just like rust, sulfation never sleeps.
>  
> -Less cells to water
>  
> -Less space required
>  
> -Given that a surprisingly high percentage of off gridders totally screw up 
> on their first bank, no matter how much we all try we might as keep the 
> stupid tax of replacing a 2.5 yr old battery bank to a minimum.
>  
> -All of this discussion about cross paralleling, buss bars, TLC with a 
> gazillion connections and multiple strings goes away.
>  
> -And the best part is we don’t have to carry all of the lead into the 
> basement and even better back out of the basement!
>  
> Just my .02.  Feel free to strongly disagree but let’s be polite about it.
>  
> Travis Creswell
> Ozark Energy Services
>  
>  
>  
> From: re-wrenches-boun...@lists.re-wrenches.org 
> [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of R Ray Walters
> Sent: Tuesday, December 01, 2009 12:44 PM
> To: RE-wrenches
> Subject: Re: [RE-wrenches] concord batteries, EQUALIZE Them!
>  
>  
> I used to think that one string was optimal; until I had a single cell 
> failure take out an entire system for weeks. (try operating a 24 v system at 
> 22v! )
> I now think that 2 parallel strings is optimum,  3 is OK, and 4 is max.
> At 4 parallel strings, we start spending more time looking to make sure all 
> connectors are the same exact length etc. to insure equal operation.
> But of course how do you account for varying internal resistance of the 
> batteries......??
> I've done 4 parallel strings at 144 DC of sealed batteries on an electric 
> vehicle, but we were very careful with our resistances, I even switched to 
> smaller wire, on closer strings, and calculated out the exact resistance, so 
> all strings were theoretically equal. This set actually just died, but 
> achieved its manufacturer's predicted cycle life. (B&B battery, 350 cycles to 
> 80% DOD)
> So if you're careful, 4 strings can work well.
> Worst I've seen was 20 golf carts paralleled in a 12 v system, (10 strings) 
> and they didn't pull the main connections from across the set, just connected 
> to one end.
> The results were very predictable, with the furthest batteries being 
> chronically under charged, and the closest ones being over cycled to a 
> premature death.
>  
> Ray Walters
>  
>  
> On Dec 1, 2009, at 11:28 AM, wind...@wind-sun.com wrote:
> 
> 
> You gotta wonder about why the customer bought such a battery layout, or why 
> the installer sold that kind of configuration (which ever it was) with so 
> many small batteries. We would never recommend going over 2 parallel banks, 
> but sometimes the "customer knows best...".
>  
>  
> _______________________________________________
> List sponsored by Home Power magazine
> 
> List Address: RE-wrenches@lists.re-wrenches.org
> 
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: 
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out participant bios:
> www.members.re-wrenches.org
> 

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org