If your talking about conduit runs between arrays, we've always used minerallac clamps to attach to either the riser, or the frame, depending on the tilt angle and accessibility. The inspector has always accepted this as bonding between arrays.....
Max Balchowsky SEE Systems 760-403-6810 ________________________________ From: Drake Chamberlin <drake.chamber...@redwoodalliance.org> To: RE-wrenches <re-wrenches@lists.re-wrenches.org> Sent: Sunday, October 11, 2009 7:38:28 AM Subject: Re: [RE-wrenches] Rooftop wiring methods between multiple subarrays At 02:35 PM 10/10/2009, you wrote: . How do we bond both ends of >the conduit? How about using a water pipe clamps on the EMT. A bare copper, # 6 or larger, should be able to be run outside the conduit, as it is a bond between sub arrays. My reading is that, from the combiner box on, an equipment grounding conductor would need to be inside the conduit. Drake Chamberlin Athens Electric OH License 44810 CO License 3773 NABCEP TM Certified PV Installer Office - 740-448-7328 Mobile - 740-856-9648
_______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org