If all you are doing in supporting the conductors, PVC conduit is sufficient 
with protective bushings on each end. Once you go to EMT, then grounding 
bushings must be installed at both ends and the EGC needs to pick up those 
bushings. More expensive and time consuming, but it looks better and you can 
span a greater distance. 

 

Bill.

 

From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Max Balchowsky
Sent: Thursday, October 08, 2009 8:29 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Rooftop wiring methods between multiple subarrays

 

August - we've been using 1/2" emt between arrays with plastic bushings to 
protect wires and a dual "minerallac" clamps ( 
http://minerallac.thomasnet.com/viewitems/pipe-fasteners/ll-categories-cully-pipe-fasteners-conduit-hangers?
 
<http://minerallac.thomasnet.com/viewitems/pipe-fasteners/ll-categories-cully-pipe-fasteners-conduit-hangers?&bc=100%7C1006%7C1281&forward=1>
 &bc=100|1006|1281&forward=1) to tie the conduits to the riser on the array 
support. Has worked well over the years and the inspectors like the "bond" 
between the arrays.....

Max Balchowsky
SEE Systems
760-403-6810

 

  _____  

From: August Goers <aug...@luminalt.com>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Sent: Thursday, October 8, 2009 11:07:08 AM
Subject: [RE-wrenches] Rooftop wiring methods between multiple subarrays




Hi Wrenches,

 

I’m looking for fresh ideas on how to run USE-2 wires between subarrays on 
rooftops. Let’s say we have a flat roof commercial system with dozens of 
separate rows of modules. How would you folks run the USE-2 wiring between 
these arrays? We’ve been using J-boxes and EMT which is robust but time 
consuming. I’ve also used strut with a cap strip on the top which effectively 
makes a wire raceway but it is difficult to properly ground both ends of the 
raceway and is also time consuming. 

 

Looking forward to hearing your ideas. Best, August 

 

August Goers

 

Luminalt Energy Corporation

O: 415.564.7652

M: 415.559.1525

F: 650.244.9167

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to