Kirpal, 

Just the other week I was faced with the exact same issue.  I spoke with
Robin over at Midnight and he confirmed that a Not-a-Gutter could be used
with four SI's.  He was sure that you could use two on top and two on the
bottom, but that did not work for me due to size restrictions.  He was then
going to look at the possibility of placing two on top and one on each end
of the gutter.  You may want to check it out!

 

Best regards,

 

Mark Dickson

Oasis Montana Inc.

 

 

  _____  

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kent
Osterberg
Sent: Wednesday, October 07, 2009 11:18 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Sunny Island DC Load Centers, Sealed Batteries

 

SMA uses a breaker for the switch in Sunny Island.  Technically, it isn't a
"disconnect" because it is part of equipment that may need to be removed for
service.

Kent Osterberg
Blue Mountain Solar, Inc


Walt Ratterman wrote: 

Hello Mick,

 

The way I understand it, the DC switch on the SI is really an on off switch
and not a circuit breaker.  SMA recommends that the system has other
overcurrent protection.  The main value of the DC switch that I could see is
that it provides an easier re-set point.  (There are some power saving
conditions that require re-setting rather than auto-re-start.)

 

And..  Since Outback has in their catalog using the Flexware mounted in this
configuration, I would say the breakers are fine to be mounted in this
fashion.  Worth checking though, of course.  I do know that you are not
supposed to mount the DC breakers upside down (such as on the bottom of the
flexware, where you would have to reach under the can to operate the
breaker...)

 

Thanks,

 

Walt

SEPI

 

 

 

From: Mick Abraham [mailto:m...@abrahamsolar.com] 
Sent: Wednesday, October 07, 2009 6:41 PM
To: wratter...@sunenergypower.com; RE-wrenches
Subject: Re: [RE-wrenches] Sunny Island DC Load Centers, Sealed Batteries

 

Hi, two questions:

(1) Doesn't each Sunny Island unit already include a DC disconnect breaker
for the connection to battery?

(2) Aren't those big DC breakers in the Outback boxes restricted for
"vertical installation only"?

I've got my own 3 phase Sunny Island thing coming up (maybe) so I look
forward to these answers.

Mick Abraham, Proprietor
www.abrahamsolar.com

Voice: 970-731-4675




On Wed, Oct 7, 2009 at 7:26 PM, Walt Ratterman
<wratter...@sunenergypower.com> wrote:

Hello Kirpal,

 

Walt Ratterman here.  I can respond to at least the first part.

 

In Burundi, we used three 5 KW Sunny Island 5048's in a three phase
configuration.  

 

For all of the DC and AC breakers, wireways, etc., etc., we used the Outback
Flexware equipment.

 

We put the DC on the bottom and the AC on the top.  Due to the width of the
SI's, we used 2 - FW1000 systems to do this.  (And I am glad - we actually
needed all of the wiring space.  I think it would work really well for your
system.

 

Of course, there may be some other good choices that I would be anxious to
learn about as well.

 

You can see some good photos of this installation at our photo gallery -
linked form our Home Page at www.sunepi.org.  Click on the cover for the
photos for the Burundi / Kigutu / Village Health Works / SELF project.

 

Feel free to holler if you need any specifics on how we did anything here.

 

OH - on your other question.I have no experience on large sealed banks, but
Rolls now has AGM's that start at T-105 size, include the 8G8D sizes, and
then go all the way up to 2V 3300 Ah.

 

Thanks!!

 

Walt

 

From: re-wrenches-boun...@lists.re-wrenches.org
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Kirpal
Khalsa
Sent: Wednesday, October 07, 2009 6:15 PM
To: RE-wrenches
Subject: [RE-wrenches] Sunny Island DC Load Centers, Sealed Batteries

 

Hi Folks......we have an upcoming Sunny Island/Sunny Boy AC Coupled system
installation.....We have mostly done Outback and Xantrex battery based
systems.......and like the available supporting DC load centers with main
breakers and other DC load and charging breakers......
What are folks using for the Sunny Island products? Outback Flexware DC
500's? or 1000's?
This particular system will consist of 4 Sunny Islands and therefore will
need four main breakers......  We primarily need a breaker box to locate our
main DC breakers coming from the battery bank.......Any advice, experiences
would be appreciated......

Also on that note.....anyone wish to share any experience or advice on the
GNB Absolyte GX series batteries or the East Penn Deka UnigyII as a standby
grid connected back up battery bank....They both seem like they are good for
primarily hanging out in float with occasional deep discharges not
negatively affecting the health of the batteries.....This is the type of
service we expect the batteries will be in primarily......Any
recommendations of one brand over the other.....The vertical stacking seems
convenient as far as space is concerned.....maintenece free......any
recommendations on a good supplier on the west coast?  Any other brands i
should be looking at in the sealed battery category for a fairly large Ah
battery bank?
100 thanks !
-- 
Sunny Regards,
Kirpal Khalsa
NABCEP Certified Solar PV Installer
Renewable Energy Systems
www.oregonsolarworks.com
541-218-0201 m
541-592-3958 o


_______________________________________________

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to