I think that the 250kW Florida Power & Light array in Sarasota, FL was
installed on a ground cover (over a landfill) like the SIT solution, and
that it was just done with PowerGuard.
-------- Original Message --------
Subject: Re: [RE-wrenches] ballasted roof rack - on the ground?
From: Joel Davidson <joel.david...@sbcglobal.net>
To: RE-wrenches <re-wrenches@lists.re-wrenches.org>
Date: 2009/8/21 10:14
Geoff,
Solar Integrated Technologies adheres its panels on ground covers
over landfills to capture landfill gases and separately produce PV
electricity. Perhaps a wrench with Powerlight experience can tell us why
rigid modules are not laid on a ground cover.
Joel Davidson
----- Original Message -----
*From:* Geoff Greenfield <mailto:ge...@third-sun.com>
*To:* RE-wrenches <mailto:re-wrenches@lists.re-wrenches.org>
*Sent:* Thursday, August 20, 2009 8:35 PM
*Subject:* [RE-wrenches] ballasted roof rack - on the ground?
esteemed wrenches (or just steamed if youve been out in the hot lately)
I'm curious why more folks don't use the same flat roof ballasted
rack approach for large ground mounts? Geotech weed barier and off
we go... my initial calcs sat its a cost saver... my instinct says
it viable, but my other instinct says "if it were this easy I would
see it all the time (and I've never seen it)
what's up? frost heave/instability? wav-i-ness of the ground?
better performance at steep angle worth all the extra cost (not
according to my pencil with today's mod costs). Thoughts?
For a brighter energy future,
Geoff Greenfield
President
Third Sun Solar & Wind Power Ltd.
340 West State Street, Unit 25
Athens, OH 45701
740.597.3111 Fax 740.597.1548
www.Third-Sun.com
Clean Energy - Expertly Installed
----- "Dave Click" <davecl...@fsec.ucf.edu> wrote:
> Thanks all.
>
> It was my understanding that we should still be running the
conductors
> of the same circuit through the same raceway, even if it is the
DC input
> into the inverter since that DC oscillates slightly (nowhere near as
> much as AC). I wasn't concerned about eddy currents in the FNMC of
> course but the metal box itself, a concern being voiced on this list
> before. I'd be more concerned about this if it were a 1MW inverter
> rather than a 7kW, but still.
>
> Thanks for the info on the GEC tap and I'm glad the split bolts
work here.
>
> The conduit in question doesn't seem to be there just for physical
> protection; the wire runs from the east end of the array for
100'+ and
> only the last 3' are in conduit. If it were only for protection
I'd be
> fine with it being open-ended on both ends, but since it's there
to feed
> the conductors into the box, that's why I was treating it as a
regular
> conduit that required a cord grip at the other end. Where do
others make
> the distinction?
>
> Thanks,
> DKC
>
> -------- Original Message --------
> Subject: Re: [RE-wrenches] DC positive and negative in same conduit,
> other inspection issues
> From: Kelly Keilwitz, Whidbey Sun & Wind <ke...@whidbeysunwind.com>
> To: RE Wrenches listserve <re-wrenches@lists.re-wrenches.org>
> Date: 2009/8/19 21:10
>
> > Dave,
> > Only GEC's are subject to the "continuous" rule (250.64C). It
sounds like
> > your are talking about an EGC tapped from the GEC.
> >
> > When splicing PV GEC's required under 690.47D, either together
(from
> > separated arrays) or to the existing AC GEC (if close enough),
we have been
> > allowed to use split bolts instead of irreversible splices, per
250.64D1,
> > "Grounding Electrode Conductor Taps" (at end of paragraph).
I.E., the
> > "continuous" rule is only being applied to the main GEC.
> >
> > I agree with Kurt on the LTNMF being used only as extra (not
required) wire
> > protection for the USE-2. We often do this when running PV
conductors
> > between short separations in modules or rails. I would think
that only
> > temperature and fill corrections would apply - and only if the
length
> > requires.
> >
> > -Kelly
> >
> > Kelly Keilwitz, P.E.
> > Whidbey Sun & Wind, LLC
> > Renewable Energy Systems
> > NABCEP Certified PV Installer
> > 987 Wanamaker Rd,
> > Coupeville, WA 98239
> > PH & FAX 360-678-7131
> > sunw...@whidbeysunwind.com
> >
> > On 8/19/09 2:41 PM, "Dave Click" <davecl...@fsec.ucf.edu> wrote:
> >
> >> For the grounding electrode wiring, it seems that it's fine to
me since
> >> they ran the continuous #6 to each rail and then to the rod,
qualifying
> >> as the 690.47(D) supplemental electrode. But the split bolts
tapping
> >> that GEC to "ground the disconnect," these are required to be
> >> irreversible connections to the ground bus in that disconnect,
right?
> >
> >
> >
> >
> >
> >
> > _______________________________________________
> > List sponsored by Home Power magazine
> >
> > List Address: RE-wrenches@lists.re-wrenches.org
> >
> > Options & settings:
> >
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> >
> > List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> >
> > List rules & etiquette:
> > www.re-wrenches.org/etiquette.htm
> >
> > Check out participant bios:
> > www.members.re-wrenches.org
> >
> >
> _______________________________________________
> List sponsored by Home Power magazine
>
> List Address: RE-wrenches@lists.re-wrenches.org
>
> Options & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out participant bios:
> www.members.re-wrenches.org
>
>
------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
------------------------------------------------------------------------
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Home Power magazine
List Address: RE-wrenches@lists.re-wrenches.org
Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out participant bios:
www.members.re-wrenches.org