I've run into this issue as well. I always keep the inverters as close to the main service panel as possible to minimize voltage problems on the AC side. The vast majority of AC voltage problems I have are when the inverters are far away from the house, and even though the wire might be oversized, breakers, bends, disconnects, etc all have a minimal resitance which can add up and require a higher output voltage from the inverter.
To reiteratate what Bill said, the inverters may say they work between 211-264V, but if you start digging deep into the manual, they have slighty smaller windows. I distinctly remember one job with two Xantrex GT inverters on a line side tap, and the grid voltage coming in was 255V. The utility company (Con Edison) said this was normal for them. Occasionally, the grid would go up to 260V, and the Xantrex would kick off. It doesn't reconnect until it hits 254V, and the grid never got down that low, so the client's inverter would be off all day long. Xantrex gave me the software and password to change the limits to 264V on the upper limit, and a reconnect voltage of 260V, which solved the problem. I've done this with Fronius inverters as well. Steven Lawrence ------------------------------ Message: 3 Date: Mon, 17 Aug 2009 09:04:46 -0700 From: "Bill Brooks" <billbroo...@yahoo.com> To: "'RE-wrenches'" <re-wrenches@lists.re-wrenches.org> Subject: Re: [RE-wrenches] utility line voltage issues Message-ID: <006d01ca1f54$728d0980$57a71c...@com> Content-Type: text/plain; charset="us-ascii" William and others, The standard requirement in IEEE929 and IEEE1547 that is tested in UL1741 is +10%/-12%. Admittedly, some utilities, particularly in more rural areas, may get close to these limits at times. Just for a little history lesson that very few people know about, this happens to be a very hard fought and won battle. Initially when IEEE929 (the original PV interconnection document) was being written, utilities wanted inverters to trip at +/- 5%. Realizing that this would be a death blow to the PV industry, several of us worked on the justification for why that did not make sense. We finally won when a key utility engineer got on our side and the proper limits went into place. The standard also recognizes that special locations, like island grids (Hawaii) and other remote grid areas may need even wider ranges to handle typical fluctuations. Widening voltage windows of the inverter requires utility permission. The voltage limits we have now are good, but most people don't understand the rest of the story. As was mentioned in the post, most PV inverters do not trip at their actually limits, they typically trip a few percent inside those limits (+8%/-10%). This is due to the difficulty of measuring ac voltage accurately, and the penalty within UL1741, the test standard, if you fail one of these limit tests. Since there is no penalty in the standard for tripping early, but a large penalty for tripping late, inverter manufacturers constrain their limits so that they trip within the limits every time, even if their transducers are at the maximum offset allowed. That is why it is so important for installers to try to stay within 1% voltage drop on the ac side. Since the utilities are allowed to go to the limits of +/-5% routinely (ANSI Range B), and outside that range for "short" periods of time (a few hours is short compared to 8760 hours), a 3% voltage drop will cause inverter tripping that is not the utility's fault--it is the installers fault. I'm not defending the utilities, but having responded to dozens of utility voltage complaints, I can say that 80-90% of the complaints were the installer's fault in having too high a voltage drop in their inverter output circuits. The legitimate issue is that PV inverters are one of the only things on the residential utility system that reacts to bad voltage. We are now placing tens of thousands of voltage sensors on the utility grid, and they will find bad places. The key is to be part of the solution, not part of the problem--keep your ac voltage drop low. For every voltage drop dollar you spend on the dc side of your design, you should put $2 toward the ac side voltage drop--it is at least twice as important because it may determine whether or not the system runs. Bill. Bill Brooks, PE Brooks Engineering 873 Kells Circle Vacaville, CA 95688 Office and Mobile: 707-332-0761 Office Fax: 707-451-7739 email: b...@brooksolar.com www.BrookSolar.com -----Original Message----- From: re-wrenches-boun...@lists.re-wrenches.org [mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Joel Davidson Sent: Sunday, August 16, 2009 1:48 PM To: RE-wrenches Subject: Re: [RE-wrenches] utility line voltage issues Correction: 4 KV ----- Original Message ----- From: "Joel Davidson" <joel.david...@sbcglobal.net> To: "RE-wrenches" <re-wrenches@lists.re-wrenches.org> Sent: Sunday, August 16, 2009 12:08 PM Subject: Re: [RE-wrenches] utility line voltage issues > Hello William, > > SCE has some 4kVA long, skinny feeders that get voltage sag during high > usage periods (August afternoons air conditioning and December nights xmas > lights and heating). High grid voltage can occur in some areas when SCE > increases the voltage to compensate for voltage sag. High grid voltage can > also occur when utility and/or customer wires are undersized. > > The CPUC, not lawyers, tell electric utilities to fix grid voltage > problems. You need to file a complaint with specific information to the > CPUC. With no PV system on and using an rms meter, measure the voltages. > Record the times and in what neighborhoods are you measure high or low > voltage. Then file a written complaint to the CPUC (contact info on the > back of an electric bill). The CPUC accept the complaint, investigate, and > tell SCE to correct the problem(s). > > If the grid voltage is within acceptable range and the grid-tie inverter > is still shutting down, then leave the inverter off and measure grid > voltage at the inverter AC in. If voltage is high, pull the grid-tie > breaker and measure grid voltage. It should be within range. If not, then > the wiring from the grid-tie breaker may be undersized or the inverter > input voltage setting may be out of range. > > Joel Davidson > > ----- Original Message ----- > From: "William Korthof" <wkort...@eesolar.com> > To: <re-wrenches@lists.re-wrenches.org> > Sent: Sunday, August 16, 2009 10:06 AM > Subject: [RE-wrenches] utility line voltage issues > > >> I'm beginning to wonder if the allowed voltage range for grid-tie >> inverters (+/-10%) is too >> sensitive in some networks and contributes more harm than benefit. This >> is close to home. >> >> Generally, the utility voltage at my house is in the mid 120's--- around >> 125 vac per phase. >> But at times, the voltage goes up higher---two weeks ago I saw 129 to >> 130V per phase. >> That voltage was high enough to put all of the inverters that I checked >> offline for much >> of the day. >> >> So I've had to call in "voltage trouble" complaints to the utility at >> least a dozen times >> over the past 5 years in response to seeing inverters offline and line >> voltage about >> 8% above nominal. ------------------------------ _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org End of RE-wrenches Digest, Vol 2, Issue 871 ******************************************* _______________________________________________ List sponsored by Home Power magazine List Address: RE-wrenches@lists.re-wrenches.org Options & settings: http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org List rules & etiquette: www.re-wrenches.org/etiquette.htm Check out participant bios: www.members.re-wrenches.org