Hi Lee,

I don't know how the two tanks are laid out physically, but if they happen to 
be installed in a way that you could run one pipeline up to the tank at 200' 
and go from there to the other tank, you might try using a float valve in the 
lower tank and a float switch in the upper tank. The lower tank's inlet would 
just be "teed" off of the pipeline going to the upper tank. The lower tank will 
fill first, being the path of least resistance. When it is full, the float 
valve closes sending water through the pipeline to the upper tank. When the 
upper tank is full, the float switch would turn the pump off.

The distance to the float switch in the upper tank is a bit far, but you should 
be OK if you use a larger gauge wire than usual. I think that 18 gauge would be 
fine, but 16 gauge would be better. If it is line-of-site, you might look into 
doing a wireless control , but that would mean that you need a small PV module 
and a battery up there.

Go with the 1 ½" pipe

Not to contradict Mark (Ok...I guess that I am!) The Grundfos model 3 SQF-3 
will do 600'

As to Allen's comment about array size, he is correct about the pump drawing a 
max of 900W. However, if you only put a 900W array on the pump, it will only 
pump at max volume at mid-day. If you put a larger array on the pump, the array 
will produce 900W in less light (morning and afternoon) and produce a lot more 
gallons per day (GPD). The GPM figure of a solar pump is really only relevant 
for making sure that you don't over pump a low yielding well. It's really GPD 
that counts. That 1.36kW array might produce 900W at 9AM and 3PM, giving you a 
solid six hours of max output pumping. No problem over sizing the array - the 
pump will only draw what it needs. If you have really good exposure to the sky, 
you can use a tracker to increase GPD instead of over sizing the PV.

According to my info, with 250" of head (220' plus pipe friction loss) you can 
get about 2000 GPD (summer) with the Grundfos model 6 SQF-2 and about 700W of 
PV in a fixed array, with a peak flow of 4.5 GPM. Adding more PV will give you 
more GPD. With the model 11 SQF-2, you can get up to about 4300 GPD with a 
1750W array at that head. If you needed even more water volume, and the well 
produced it, you could even put two pumps in the well (with separate arrays). I 
had one dealer who managed to put two Grundfos pumps down a 5" casing! He said 
that it all went easy....but I don't believe him. He did have a curious issue 
though. He said that if he turned one pump off with its CU200, both pumps would 
shut down, even though the other pump was not connected to that CU200. He 
couldn't just run one pump. I never did talk to Grundfos about that.

Cheers!

Brian Teitelbaum
AEE Solar




From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Mark Dickson
Sent: Thursday, June 11, 2009 9:40 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Design help for solar water pumping application

Hey Lee,
Allan is right in that the WINcaps software is a lifesaver and FREE!  Not to 
contradict Allan, but I do not see a feasible way of using two float switches 
in separate tanks with only one pump controller.  Also, the 3000' distance is a 
little far-they usually recommend a max distance of 1600' for the float 
switches.  Lastly, if you are ever worried about the head, the Lorentz pumps 
can pump up to 760' --more than double the recommended for Grundfos.

I highly recommend Genpro Energy Solutions as a pump distributor for both of 
those brands.  They always answer the phone, are personable and return emails 
(hint, hint Conergy)!

Best,

Mark Dickson
Oasis Montana Inc.
www.oasismontana.com<http://www.oasismontana.com/>

www.grid-tie.com<http://www.grid-tie.com/>

www.PVsolarpumps.com<http://www.pvsolarpumps.com/>
________________________________
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Allan Sindelar
Sent: Thursday, June 11, 2009 2:28 PM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Design help for solar water pumping application

Lee,
You can get Grundfos' WINCaps software from your RE or pump supplier; some will 
run the sizing for you (Jeremy at Conergy does for us). I didn't check your 
head and flow, but I would expect that's about your only good pump choice at 
that head. Add a tracker if you need greater summer output; don't attempt 
batteries as a solution. If usage occasionally exceeds output, add an IO101 
control and allow the pump to run off any AC source at night. A tiny 1,200W 
inverter/generator will work at sea level. Use a CU200 controller to allow a 
float or level detector switch to turn off the pump when tanks are full. 
Mercury-based float switches last longer in signal circuits that carry no 
current. If you can't use a float switch because the lines are already buried, 
look into www.P2Flow.com<http://www.p2flow.com/> for pressure transducer-based 
control. Read the website info, then call Britt there with your specific 
application. That array sounds oversized, as the pump draws a maximum of 900 
watts. Hope this helps.

Allan Sindelar
al...@positiveenergysolar.com<mailto:al...@positiveenergysolar.com>
NABCEP Certified Photovoltaic Installer
EE98J Journeyman Electrician
Positive Energy, Inc.
3201 Calle Marie
Santa Fe, New Mexico 87507
505 424-1112
www.positiveenergysolar.com<http://www.positiveenergysolar.com>
________________________________
From: re-wrenches-boun...@lists.re-wrenches.org 
[mailto:re-wrenches-boun...@lists.re-wrenches.org] On Behalf Of Lee Bristol
Sent: Thursday, June 11, 2009 1:26 PM
To: RE-wrenches@lists.re-wrenches.org
Subject: [RE-wrenches] Design help for solar water pumping application

Solar Water Pumping Wrenches,

We normally don't do solar water pumping but a friend asked for some help 
designing his system.  He has one well and two 5,000 gallon reservoirs to fill 
up.  The average usage is expected to be about 2,000 gallons per day but may be 
higher in the summer.  The tanks will have level detector switches to sense 
when the tank is full.  The site is near Leesburg, VA.

The problem is to design a control system to turn on the pump when one or both 
of the tanks needs water and to shut it off when both are full.  The closest 
tank has a head requirement of 200 feet (pump to tank) and is 300 feet from the 
well head.  The second tank head requirement is 220 feet and it is 3,000 feet 
from the well.  The pipes are expected to be 1.25 or 1.5 inch.

A Grundfos SQFlex 6 SQF-2 pump with 1.36 KW solar was recommended, 360 foot 
head, 360 gph.  I think that this would provide the lift but not the quantity.  
Hmmmm, what valves and controls would you all suggest?

Thanks!
Lee

--
Lee Bristol
NABCEP Certified Solar Designer/Installer

Chief Technology Officer
Standard Solar, Inc.
202 Perry Parkway, #7
Gaithersburg, MD 20877
(301) 944-5105
(240) 479-1510 (c)
www.standardsolar.com<http://www.standardsolar.com>
_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to