Hello Kurt,

Thanks for looking at this problem.

The project manager works for a licensed PV contracting company that has been 
trying for several months to get this PV system approved. First, they were 
blocked by the Los Angeles Building & Planning's interpretation of the LA Fire 
Marshall's set-back guidelines (not regulations). Now LADWP's interconnection 
department is holding up the project. If the system had been installed last 
year as planned, this new rule would not have applied. There is no requirement 
like this in nearby Southern California Edison (SCE) territory.

(Pulling the meter is not acceptable to most fire departments, but that's a 
separate subject.)

My question is Do any other electric utilities require an additional disconnect 
switch on a PV system with a line-side tap?

Joel Davidson 

  ----- Original Message ----- 
  From: Kurt Albershardt 
  To: RE-wrenches 
  Sent: Saturday, February 21, 2009 12:08 PM
  Subject: Re: [RE-wrenches] 2 PV utility interconnect disconnects?


  On 2/21/09 10:24 AM, Joel Davidson wrote: 
    January 1, 2009 LADWP added another interconnection requirement. See page 
8-11 at http://www.ladwp.com/ladwp/cms/ladwp004344.pdf


  I found what I think is the relevant section on p. 36 of the PDF (called out 
as p. 1-32 at the top of the page.)



    This is how a PV commercial project manager described this new requirement:

  I'm curious if this was an LADWP project manager, or someone managing 
projects for customers?



    When a customer, any customer, generates electrical power with the 
intention of supplying that power to the electrical grid, the connection to the 
grid has to be made below, or on the load-side, of one main switch for the 
property.

  They define

  generators using a closed-transition (“make-before-break”) type transfer 
switch or a multi- 
  breaker transfer scheme, or an electrical inverter that can be configured to 
operate in a utility 
  interactive mode constitute a potential back feed source into the 
Department’s electric system and are 
  classified as interactive generators.



    the policy seems to be that the total electricity supplied to any building 
or property must be disconnected from the grid by one main switch.

  The wording appears to be:

   All interconnected generating systems shall be connected on the load side of 
the customer’s meter switch (main service disconnect device). 

  I'm wondering about the origins of this requirement.  How would they handle 
critical power systems (data centers, hospitals, etc. which are often fed by 
multiple services entering by different routes?)  How would they handle a 
premises with multiple service voltages?




    This policy is in place for emergency situations, to where fire fighters or 
persons on the scene during an emergency would be able to completely shut down 
building power with one switch. 

  The phrase "pull the meter" comes to mind here...




    This describes a scenario whereby the grid is disconnected from the 
building circuits, but the solar PV is still connected to the building 
circuits. Therefore, there is a basic flaw in this requirement; this scenario 
is only possible at nighttime- during the daytime, the solar PV system is 
energized and may still feed to the building electrical circuits, unless the 
main PV disconnect switch is opened.


  Has this "project manager" ever heard of anti-islanding?  This fantasy 
scenario almost makes sense for a battery-backed PV system, but then the 
presence or absence of sunshine would not matter.  What about emergency backup 
gensets and UPS or flywheel systems?  They are protected from backfeeding by a 
transfer switch, so exempted, but UL 1741 does not qualify as such?











------------------------------------------------------------------------------


  _______________________________________________
  List sponsored by Home Power magazine

  List Address: RE-wrenches@lists.re-wrenches.org

  Options & settings:
  http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

  List-Archive: 
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

  List rules & etiquette:
  www.re-wrenches.org/etiquette.htm

  Check out participant bios:
  www.members.re-wrenches.org

_______________________________________________
List sponsored by Home Power magazine

List Address: RE-wrenches@lists.re-wrenches.org

Options & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
www.re-wrenches.org/etiquette.htm

Check out participant bios:
www.members.re-wrenches.org

Reply via email to