Code requires this here.  The intent of the EPO buttons are to immediately 
disconnect all energized power to the entire facility/building in the event of 
a critical fault like an electrical fire or electrocution. 

Only locally-battery powered low-voltage emergency lighting should still be 
operating.   Often the next step after EPO is to flood the room...
—L.B.

Ms. Lady Benjamin PD Cannon of Glencoe, ASCE
6x7 Networks & 6x7 Telecom, LLC 
CEO 
l...@6by7.net <mailto:l...@6by7.net>
"The only fully end-to-end encrypted global telecommunications company in the 
world.”
FCC License KJ6FJJ



> On Sep 15, 2021, at 8:58 AM, Adam Thompson <athomp...@merlin.mb.ca> wrote:
> 
> Now I'm curious... in all of the DCs and COs I've worked in - to the best of 
> my knowledge, I haven't personally tested this! - the EPO button does not​ 
> switch to emergency power.  It turns off ALL equipment power in the space - 
> no lights, no klaxons, nothing.  In simpler setups, the EPO is connected to 
> the UPS so anything plugged in to the UPS does dark instantly.  In one DC I'm 
> familiar with, the EPO switch kills all the UPS output and​ uses several 
> relays to kill commercial power at the same time.
> In some, the room lights were not covered by the EPO switch, in some they 
> were.  Emergency exit lamps will continue to be lit, as they have internal 
> batteries, and are required by building/fire code.
> 
> Is it (somewhat) common for an EPO switch to only disconnect commercial power 
> and leave local redundant power live?  What sort of facilities would have 
> this?
> 
> -Adam
> 
> Adam Thompson
> Consultant, Infrastructure Services
> 
> 100 - 135 Innovation Drive
> Winnipeg, MB, R3T 6A8
> (204) 977-6824 or 1-800-430-6404 (MB only)
> athomp...@merlin.mb.ca <mailto:athomp...@merlin.mb.ca>
> www.merlin.mb.ca <http://www.merlin.mb.ca/>
> From: NANOG <nanog-bounces+athompson=merlin.mb...@nanog.org> on behalf of Jay 
> R. Ashworth <j...@baylink.com>
> Sent: September 11, 2021 22:23
> To: nanog <nanog@nanog.org>
> Subject: Re: Never push the Big Red Button (New York City subway failure)
>  
> ----- Original Message -----
> > From: "Sean Donelan" <s...@donelan.com>
> 
> > NEW YORK CITY TRANSIT RAIL CONTROL CENTER POWER
> > OUTAGE ISSUE ON AUGUST 29, 2021
> > Key Findings
> > September 8, 2021
> > 
> > https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf
> >  
> > <https://www.governor.ny.gov/sites/default/files/2021-09/WSP_Key_Findings_Summary-for_release.pdf>
> > 
> > Key Findings
> > [...]
> > 
> > 3. Based on the electrical equipment log readings and the manufacturer’s
> > official assessment, it was determined that the most likely cause of RCC
> > shutdown was the “Emergency Power Off” button being manually activated.
> 
> I don't even *do* datacenter for a living, and I know that when you hit the
> Molly button, 
> 
> 1) A Klaxon goes off in the Data Center -- one that sounds *different* from
> the Halon Klaxon, in both cadence and tone (just for a couple bursts), and
> 
> 2) Yellow rotating beacons turn on, and stay on while you're on Emergency 
> Power.
> 
> Yes, real honest-to-ghod *rotating mechanical beacons*, none of this flashing 
> LED
> crap.
> 
> Clearly, it's important that the use of Emergency Power be annoyingly 
> noticeable.
> 
> Cheers,
> -- jra
> -- 
> Jay R. Ashworth                  Baylink                       
> j...@baylink.com
> Designer                     The Things I Think                       RFC 2100
> Ashworth & Associates       http://www.bcp38.info <http://www.bcp38.info/>    
>       2000 Land Rover DII
> St Petersburg FL USA      BCP38: Ask For It By Name!           +1 727 647 1274

Reply via email to