David Christensen wrote:
For the record we also have not been able to reproduce the issue on
the R710 only the R610.
I got hold of an R610 system and I now understand why the
issue was difficult to replicate on R710. The R610 ships
without Enterprise iDRAC while the R710 ship with the add-in
Enterprise iDRAC module. When the module is present the
system is managed through the additional RJ45 port but when
the module is absent iDRAC traffic will flow through the
on-board 5709 adpaters.
The error will only occur when management firmware is loaded
on the 5709 AND when NC-SI management functionality is enabled.
You should be able to confirm this by adding or removing the
Enterprise iDRAC module on your systems. Now that I have a
failure again I have some ideas to test which might help.
Stay tuned.
Does the attached patch make a difference for you?
FYI, I'll be out next week on vacation.
Hi David,
This patch seems to do the trick, on at least one of the R610's that we
have.
Just did cold boot, 5 warm boots, cold boot, 5 warm boots and have not
had any issues.
Thanks
Tom