David Christensen wrote:
For the record we also have not been able to reproduce the issue on the R710 only the R610.
I got hold of an R610 system and I now understand why the issue was difficult to replicate on R710. The R610 ships without Enterprise iDRAC while the R710 ship with the add-in Enterprise iDRAC module. When the module is present the system is managed through the additional RJ45 port but when the module is absent iDRAC traffic will flow through the on-board 5709 adpaters. The error will only occur when management firmware is loaded on the 5709 AND when NC-SI management functionality is enabled.

You should be able to confirm this by adding or removing the Enterprise iDRAC module on your systems. Now that I have a failure again I have some ideas to test which might help.
Stay tuned.

Does the attached patch make a difference for you?

FYI, I'll be out next week on vacation.


Hi David,

This patch seems to do the trick, on at least one of the R610's that we have.

Just did cold boot, 5 warm boots, cold boot, 5 warm boots and have not had any issues.


Thanks

Tom
_______________________________________________
freebsd-net@freebsd.org mailing list
http://lists.freebsd.org/mailman/listinfo/freebsd-net
To unsubscribe, send any mail to "freebsd-net-unsubscr...@freebsd.org"