Internationally, this type of protection is provided by a Residual Current
Device. Application note from Eaton here
<https://www.eaton.com/content/dam/eaton/products/electrical-circuit-protection/circuit-breakers/xeffect-rccb/eaton-rcd-application-guide-br019003en-en-us.pdf>
that should be helpful. See IEC 61008-1
<https://webstore.iec.ch/publication/4264> and/or IEC 61009-1
<https://webstore.iec.ch/publication/4273>.

On Mon, Nov 27, 2023 at 6:18 AM Ronan Shanley <
[email protected]> wrote:

> Thanks Richard,
>
>
>
> Looking UL-943 the voltage ranges outlined cap out at 120/240 VAC. Does
> anyone know if GFCI standards for higher voltages like 400/230 VAC exist?
>
>
>
> Best,
>
>
>
> Ronan
>
>
>
> *From:* Richard Nute <[email protected]>
> *Sent:* Tuesday, November 21, 2023 3:18 PM
> *To:* Ronan Shanley <[email protected]>;
> [email protected]
> *Subject:* RE: [PSES] American Vs. European 30 Ground Fault Leakage
> Current Standards
>
>
> [EXTERNAL]
>
>
>
> Hi Ronan:
>
>
>
> GFEP North America:
>
> https://www.eaton.com/us/en-us/skuPage.GFEP130.pdf
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__www.eaton.com_us_en-2Dus_skuPage.GFEP130.pdf&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=yG7zFfFYJf5TmIkJ-eeYmawQKncirVqCiwrZOGH86XpaIs8LlOYdSHyCznhhMWI6&m=8ip0moSdrMlLkpXo2MmAGhOi5RDgtEbZPYq5nYx_kSwBA2OmVYaXt-Qm9C2lzuMz&s=8IIZ9S0pF6IITwMnUaaWgwyJtLKJ27Bvob0ztcckfTs&e=>
>
>
>
> GFEP Europe:
>
>
> https://library.e.abb.com/public/a9cd966c1794415d945b232fb2d7a9ee/1SXU430091L0201_GFEP_Info_Tool.pdf
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__library.e.abb.com_public_a9cd966c1794415d945b232fb2d7a9ee_1SXU430091L0201-5FGFEP-5FInfo-5FTool.pdf&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=yG7zFfFYJf5TmIkJ-eeYmawQKncirVqCiwrZOGH86XpaIs8LlOYdSHyCznhhMWI6&m=8ip0moSdrMlLkpXo2MmAGhOi5RDgtEbZPYq5nYx_kSwBA2OmVYaXt-Qm9C2lzuMz&s=y7hxsn9vhqB90df2cx7Ga6KvC7gCX3RRQHiTnY9isGM&e=>
>
>
>
> According to:
>
> https://forums.mikeholt.com/threads/gfci-vs-gfep.116424/
> <https://urldefense.proofpoint.com/v2/url?u=https-3A__forums.mikeholt.com_threads_gfci-2Dvs-2Dgfep.116424_&d=DwMFAg&c=euGZstcaTDllvimEN8b7jXrwqOf-v5A_CdpgnVfiiMM&r=yG7zFfFYJf5TmIkJ-eeYmawQKncirVqCiwrZOGH86XpaIs8LlOYdSHyCznhhMWI6&m=8ip0moSdrMlLkpXo2MmAGhOi5RDgtEbZPYq5nYx_kSwBA2OmVYaXt-Qm9C2lzuMz&s=pJd0a4XsP_11t5dUduoxP0TMVMDQiHslgFW7p_lWeqk&e=>
>
> “GFCI and GFPE have different trip thresholds and GFPE is for protecting
> equipment not humans.”
>
>
>
> Richard
>
> Bend, Oregon
>
>
>
>
>
> *From:* Ronan Shanley <[email protected]>
> *Sent:* Tuesday, November 21, 2023 11:37 AM
> *To:* [email protected]
> *Subject:* [PSES] American Vs. European 30 Ground Fault Leakage Current
> Standards
>
>
>
> Hello Experts,
>
>
>
> Does anyone know if a GFEP breaker, that meets the USA standards, will
> meet the EU standard for human protection? If not, why is that? What is the
> difference between the USA and EU standards?
>
>
>
> Best,
>
>
>
> *Ronan Shanley*
>
> Automation Engineer
> SIO Electrical
>
>
>
>
>
> This message (including any attachments) may be confidential and
> privileged communication to the intended addressee. If you are not the
> intended addressee, you have received this message in error. In that case,
> please permanently delete this message and notify us at
> [email protected] so that we can avoid this
> inconvenience in the future. Thank you.
> ------------------------------
>
> This message is from the IEEE Product Safety Engineering Society emc-pstc
> discussion list. To post a message to the list, send your e-mail to All
> emc-pstc postings are archived and searchable on the web at:
> https://www.mail-archive.com/[email protected]/
>
> Website: https://ewh.ieee.org/soc/pses/
> Instructions: https://ewh.ieee.org/soc/pses/list.html (including how to
> unsubscribe) <https://ewh.ieee.org/soc/pses/list.html>
> List rules: https://ewh.ieee.org/soc/pses/listrules.html
>
> For help, send mail to the list administrators:
> Mike Sherman at: [email protected]
> Rick Linford at: [email protected]
>
> For policy questions, send mail to:
> Jim Bacher at: [email protected]
> ------------------------------
>
> To unsubscribe from the EMC-PSTC list, click the following link:
> https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1
>


-- 
Scott Aldous | Regulatory Compliance Manager | [email protected] |
 650-253-1994

-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
https://www.mail-archive.com/[email protected]/

Website:  https://ewh.ieee.org/soc/pses/
Instructions:  https://ewh.ieee.org/soc/pses/list.html (including how to 
unsubscribe)
List rules: https://ewh.ieee.org/soc/pses/listrules.html

For help, send mail to the list administrators:
Mike Sherman at: [email protected]
Rick Linford at: [email protected]

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
_________________________________________________
To unsubscribe from the EMC-PSTC list, click the following link: 
https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to