If you are declaring conformance with the EU’s EMC Directive, there are standard surge tests to run. There are generic “light industrial” and “heavy industrial” levels of surge immunity. As shorthand, “heavy” can be interpreted as a facility with its own pad transformer, and “light” as one that shares a utility transformer with others (think strip mall). 
There’s also a “fast transient” test, as I recall. That might be related to lighting strikes, but there are others on this forum who know this better than I. 

Mike Sherman 
Sherman PSC LLC
On 11/02/2022 1:59 PM Brian Kunde <[email protected]> wrote:


Very good information, all. 

So how do I know if my product is "effectively protected from voltage surges on the incoming supply circuit"??
Can I test my product to the Surge Immunity Test IEC 61000-4-5 at some voltage??? 2kV?, 3kV? 4kV? higher? to make that determination? 

How is a Field Inspector going to determine if a product is efficiently protected or not?  

The manufacturers of Surge Protection Devices are saying their "listed" devices are now "Required", and there's no way around it. The hair on the back of my head sticks up when I hear such things.  

Manufacturers of Industrial Machines will not know if their customer already has Surge Protection, so why should the both parties be burdened with the cost of double protection. Can the machine manufacturer specify that the facility must provide the SPD?  

Instead of just requiring a SPD, why not require the Machine Manufacturer to insure their products pass a Surge Immunity Test of some kind? Isn't Surge Immunity already a requirement in the electrical safety standards that Machines have to meet anyway?  

You got me thinking, now. Thanks again. 
Brian    


On Tue, Nov 1, 2022 at 5:26 PM Don Gies <[email protected]> wrote:

Group,

 

The requirement for surge protection in NFPA 70 (2023): 670.6 goes back to NFPA 79, “Electrical Standard for Industrial Machinery.”

 

 

The scope NEC 70 (2023): 670  refers to NFPA 79, as follows:

 

Article 670 Industrial Machinery

670.1 Scope.

This article covers the nameplate data for, overvoltage protection for, and the size and overcurrent protection of supply conductors to industrial machinery.

Informational Note No. 1:
See NFPA 79, Electrical Standard for Industrial Machinery, for further information.

Informational Note No. 2:
See 110.26 for information on the workspace requirements for equipment containing supply conductor terminals.

Informational Note No. 3:
See NFPA 79, Electrical Standard for Industrial Machinery, for information on the workspace requirements for machine power and control equipment.

670.6 reads as follows (2023 NEC):

670.6 Overvoltage Protection.
Industrial machinery with safety circuits shall have overvoltage protection.

 

Under NFPA 79:  7.8.1, the requirement for surge protection is as follows:

 

7.8.1* Surge-Protective Devices (SPDs).

Industrial machinery with safety circuits not effectively protected from the effects of overvoltages due to lightning or switching surges shall have surge protection installed.

Exception:
SPDs shall not be required where the risks associated with the effects of overvoltages are mitigated such that the safety performance determined by a risk assessment is met.

Enhanced Content

The term surge-protective devices (SPDs) has replaced the previously used terms overvoltage protection device, lightning overvoltage suppression, and surge switching overvoltage suppression in 7.8.1, 7.8.2, and 7.8.3. See the definition of surge-protective device (SPD) in 3.3.104. The 2018 edition revised the existing requirement in 7.8.1 to require an appropriate SPD for protection of industrial machinery with safety interlock circuits to correlate with Section 670.6 of NFPA 70.

 

 

Best regards,

Don Gies


 

 

 

Internal

From: Richard Nute <[email protected]>
Sent: Tuesday, November 1, 2022 4:03 PM
To: [email protected]
Subject: Re: [PSES] Surge Protection Device required by NEC

 

[External email: Use caution with links and attachments]


 

 

The NEC 670.6 quote triggers some questions:

 

I wonder why industrial machinery with a safety interlock is required to have surge protection as opposed to machinery that does not have an interlock?

 

Is an “on-off” or “run-stop” control considered a “safety interlock”?

 

Is the “surge” a higher-than-normal power-line voltage or is it an impulse from switching or lightning?

 

Does “effectively protected” mean passing the dielectric (hi-pot) test?

 

Richard Nute

Bend, Oregon, USA

(Several inches accumulation of snow this morning, but above freezing.)

 

 

From: Doug Powell <[email protected]>
Sent: Tuesday, November 1, 2022 11:28 AM
To: [email protected]
Subject: Re: [PSES] Surge Protection Device required by NEC

 

From the 2020 Edition, emphasis is mine.

 

"670.6 Surge Protection. Industrial machinery with safety interlock control devices not effectively protected from voltage surges on the incoming supply circuit shall have surge protection installed."

 

It does not say where this protection needs to be applied, so I assume it can be within the machine or somewhere in machine supply. Also, does the product you are inquiring about fall under the definition of Industrial Machinery, NFPA 79? 

 

-Doug

 

Douglas E Powell

Laporte, Colorado USA

 

(UTC -06:00) Mountain Time (US-MDT)

 

 

 

On Tue, Nov 1, 2022 at 11:55 AM Brian Kunde <[email protected]> wrote:

It just came to my attention that section 670.6 of the US National Electric Code 2017 requires a listed Surge Protection Device (SPD) to be on any Industrial Machine that has an Interlock, or I assume any kind of safety function.  Is this true? The only information I can find on the internet is from the companies that make and sell the SPDs which can often be very one sided.  Is there more to this story that I am missing?

 

Does the Surge Protection have to be listed? Are there specifications for the SPD? Is there a Surge Immunity Test that be used to validate and verify whether an additional SPD is required or not?  

 

Thanks,

The Other Brian

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]>


To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to &LT;[email protected]&GT;

All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Mike Cantwell &LT;[email protected]&GT;

For policy questions, send mail to:
Jim Bacher &LT;[email protected]&GT;
David Heald &LT;[email protected]&GT;


To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]>


To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

-
----------------------------------------------------------------

This message is from the IEEE Product Safety Engineering Society emc-pstc discussion list. To post a message to the list, send your e-mail to <[email protected]>

All emc-pstc postings are archived and searchable on the web at: http://www.ieee-pses.org/emc-pstc.html

Website: http://www.ieee-pses.org/
Instructions: http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher <[email protected]>
David Heald <[email protected]>


To unsubscribe from the EMC-PSTC list, click the following link: https://listserv.ieee.org/cgi-bin/wa?SUBED1=EMC-PSTC&A=1

Reply via email to