We did some EMC testing last week (radiated emission in a chamber) on a 
ventilation system with two fans. It exceeded the limits on 145MHz. 

 

Then outside the camber, we shut down the fans, we found the 145MHz on a bus 
line from a controller (3rd part product). Connecting the fans back again, the 
noise increase with increasing speed on the fans. Broadband noise at 145MHz.

 

The troubleshooting process have been carried out outside the chamber (due to 
costs). We had a current clamp connected to a spectrum analyzer and measured 
every internal cable.

145MHz was only visible on the bus line and the cables to the fans (which are 2 
meters long, unshielded).

 

We inserted a CM choke on the bus line, and the 145MHz on the fan cable 
decreased by approximate 5 dB (current clamp meas.). What this would mean in 
decreased level under a radiated test, it’s hard to say.

 

We are planning to check it out in the chamber next time.

During that exercise, we will also prepare a better bonding of the fan cables 
to the chassis in order to reduse the radiated fields from the fan cables. Also 
have a shielded harness.

 

Do you agree that the current clamp + spectrum analyzer, is a good tool for 
finding the noise and the wires that may act as antennas?

 

 

Best regards

Amund 

 

 

 


-
----------------------------------------------------------------
This message is from the IEEE Product Safety Engineering Society emc-pstc 
discussion list. To post a message to the list, send your e-mail to 
<[email protected]>

All emc-pstc postings are archived and searchable on the web at:
http://www.ieee-pses.org/emc-pstc.html

Attachments are not permitted but the IEEE PSES Online Communities site at 
http://product-compliance.oc.ieee.org/ can be used for graphics (in well-used 
formats), large files, etc.

Website:  http://www.ieee-pses.org/
Instructions:  http://www.ieee-pses.org/list.html (including how to unsubscribe)
List rules: http://www.ieee-pses.org/listrules.html

For help, send mail to the list administrators:
Scott Douglas <[email protected]>
Mike Cantwell <[email protected]>

For policy questions, send mail to:
Jim Bacher:  <[email protected]>
David Heald: <[email protected]>

Reply via email to