> On May 4, 2017, at 11:54 AM, Jon Elson via cctalk <cctalk@classiccmp.org> 
> wrote:
> 
> ...  But, you DO need a true sine wave source, and VFDs do not produce sine 
> waves, they put out 400 V PWM waveforms that look fine to a motor, but not 
> good at all to electronic loads.

I wonder how true that is.  Consider that (for machines of this era) power 
supplies are probably transformer input, to a rectifier and then a filter.  The 
transformer would smooth out the VFD output pulses, and whatever is left would 
definitely be removed by the output filter.  The only question I can see is 
whether the rectifier diodes have enough reverse voltage margin to deal with 
whatever peaks pass through the transformer.  (The transformer itself certainly 
will, given normal insulation design/test practice for power transformers.)

If the power supply is a swiching regulator, the details are slightly different 
but the overall picture is similar.  Then you begin with a rectifier, which 
would have to be able to deal with the input spikes, followed by some amount of 
filtering.  Once past that I don't see any further issues.

An electronic circuit that looks at the incoming AC waveform directly would 
certainly have issues with a VFD, but I can't think of too many examples of 
that.  A KW-11/L is one exception that comes to mind... :-)

        paul