Southwire says low probability of jam. I just don’t believe it. This is 480 volts. 250 amps. Probably don’t need the neutral. For my conduit extruder line.
Last time I priced aluminum, since it had to be larger, the cost was similar. That was at Home Depot though. From: Forrest Christian (List Account) Sent: Friday, May 27, 2022 2:57 PM To: AnimalFarm Microwave Users Group Cc: Chuck McCown Subject: Re: [AFMUG] Conduit Fill I hate running copper that big so I haven't pulled that much. I try to contract that out if possible. I do find that the jam probably on the southwire wire fill calculator is helpful as it gives a likihood of wires getting stuck. Just curious what are you powering that needs 4/0 copper? That's a lot of power. If this is this 120/208 is moving to 277/480 a possibility? (And if this is 480V, I'm really curious about what you're hooking up) And do you really need a neutral? One note is that aluminum is a fair bit easier to pull and has similar ampacity at the larger sizes. Plus it's a lot cheaper. On Fri, May 27, 2022, 2:13 PM Chuck McCown via AF <af@af.afmug.com> wrote: I gotta run 4 x 4/0 copper THHN and one #6 to a machine. The online raceway calculators say I can do this with 2” conduit. I will have two sweeps and at least 2 LBs. As much as I hate to, I really think I should use larger conduit. I really hate it when I have trouble pulling larger cables in too small of a conduit. Any raceway fill experts on here? -- AF mailing list AF@af.afmug.com http://af.afmug.com/mailman/listinfo/af_af.afmug.com