Southwire says low probability of jam.  I just don’t believe it.  
This is 480 volts.  250 amps.  Probably don’t need the neutral.  
For my conduit extruder line.  

Last time I priced aluminum, since it had to be larger, the cost was similar.  
That was at Home Depot though.  

From: Forrest Christian (List Account) 
Sent: Friday, May 27, 2022 2:57 PM
To: AnimalFarm Microwave Users Group 
Cc: Chuck McCown 
Subject: Re: [AFMUG] Conduit Fill

I hate running copper that big so I haven't pulled that much.   I try to 
contract that out if possible.   I do find that the jam probably on the 
southwire wire fill calculator is helpful as it gives a likihood of wires 
getting stuck. 

Just curious what are you powering that needs 4/0 copper?   That's a lot of 
power.    If this is this 120/208 is moving to 277/480 a possibility?  (And if 
this is 480V, I'm really curious about what you're hooking up)   And do you 
really need a neutral? 


One note is that aluminum is a fair bit easier to pull and has similar ampacity 
at the larger sizes.   Plus it's a lot cheaper. 



On Fri, May 27, 2022, 2:13 PM Chuck McCown via AF <af@af.afmug.com> wrote:

  I gotta run 4 x 4/0 copper THHN and one #6 to a machine.  

  The online raceway calculators say I can do this with 2” conduit.  

  I will have two sweeps and at least 2 LBs.  As much as I hate to, I really 
think I should use larger conduit.  I really hate it when I have trouble 
pulling larger cables in too small of a conduit.  

  Any raceway fill experts on here?
  -- 
  AF mailing list
  AF@af.afmug.com
  http://af.afmug.com/mailman/listinfo/af_af.afmug.com
-- 
AF mailing list
AF@af.afmug.com
http://af.afmug.com/mailman/listinfo/af_af.afmug.com