Le 2013-01-29 21:02, Ralph Castain a écrit :

On Jan 28, 2013, at 10:53 AM, Maxime Boissonneault <maxime.boissonnea...@calculquebec.ca <mailto:maxime.boissonnea...@calculquebec.ca>> wrote:

While our filesystem and management nodes are on UPS, our compute nodes are not. With one average generic (power/cooling mostly) failure every one or two months, running for weeks is just asking for trouble. If you add to that typical dimm/cpu/networking failures (I estimated about 1 node goes down per day because of some sort hardware failure, for a cluster of 960 nodes). With these numbers, a job running on 32 nodes for 7 days has a ~35% chance of failing before it is done.

I've been running this in my head all day - it just doesn't fit experience, which really bothered me. So I spent a little time running the calculation, and I came up with a number much lower (more like around 5%). I'm not saying my rough number is correct, but it is at least a little closer to what we see in the field.

Given that there are a lot of assumptions required when doing these calculations, I would like to suggest you conduct a very simply and quick experiment before investing tons of time on FT solutions. All you have to do is:

Thanks for the calculation. However, this is a cluster that I manage, I do not use it per say, and running such statistical jobs on a large part of the cluster for a long period of time is impossible. We do have the numbers however. The cluster has 960 nodes. We experience roughly one power or cooling failure per month or two months. Assuming one such failure per two months, if you run for 1 month, you have a 50% chance your job will be killed before it ends. If you run for 2 weeks, 25%, etc. These are very rough estimates obviously, but it is way more than 5%.

In addition to that, we have a failure rate of ~0.1%/day, meaning that out of 960, on average, one node will have a hardware failure every day. Most of the time, this is a failure of one of the dimms. Considering each node has 12 dimms of 2GB of memory, it means a dimm failure rate of ~0.0001 per day. I don't know if that's bad or not, but this is roughly what we have.
If it turns out you see power failure problems, then a simple, low-cost, ride-thru power stabilizer might be a good solution. Flywheels and capacitor-based systems can provide support for momentary power quality issues at reasonably low costs for a cluster of your size.
I doubt there is anything low cost for a 330 kW system, and in any case, hardware upgrade is not an option since this a mid-life cluster. Again, as I said, the filesystem (2 x 500 TB lustre partitions) and the management nodes are on UPS, but there is no way to put the compute nodes on UPS.

If your node hardware is the problem, or you decide you do want/need to pursue an FT solution, then you might look at the OMPI-based solutions from parties such as http://fault-tolerance.org or the MPICH2 folks.
Thanks for the tip.

Best regards,

Maxime