On Wed, Nov 17, 2010 at 10:35 PM, Singer Wang <[email protected]> wrote:
>
>
> On Wed, Nov 17, 2010 at 7:59 PM, Doug Hughes <[email protected]> wrote:
>>
>> I'll reemphasize some earlier points and make some of my own.
>>
>> On 11/17/2010 11:37 AM, Daniel Clark wrote:
>> > Looking for a UPS system that:
>> >
>> > 1. Runs off of US 115V / 20A
>> That isn't much power. Remember, you can only use 16A of a 20A circuit,
>> that limits the size of your UPS and your load to about 1.8KW. That's
>> not a heckuva a lot. I'd definitely recommend at least going to 220V (or
>> 208V, depending upon your building electric power plant)
>> > 2. Can handle frequent extended power outages while continuing to
>> > provide power to computers and HVAC systems (so amp spikes will be
>> > common)
>> add batteries for run time. Just remember, the more batteries you have
>> and the closer you get it to specifications, the longer it's going to
>> take to charge that baby.
>> I'd give at least a 20% leeway on the input side.
>>
> Acutally more about 1.2KW if you think the best case. He's estimating a 16
> hour charge cycle followed by a 8 hour discharge cycle. So during the 16
> hour charge cycle, the 115V/20A must charge the battery as well as provide
> for the HVAC and the computer. Since there's a 2-1 ratio of charge vs
> discharge time, out of your 1.8KW you have to give at least 0.6KW  to
> charging the battery (all best case).

BTW found something that may work great (or at least as well as
possible given site limitations) -
http://www.bdbatteries.com/upskits.php?id=293

An important point is that you can set the current it uses to any
arbitrary value between 0 and 20 amps, amongst other niftyness.

Haven't been able to find any 3rd party discussion of the system
however... If I end up going with it I'll be sure to report
experiences here.

Thanks for the above info as well, very very useful.

Cheers,
--
        \|/      Daniel JB Clark | Activist; Owner
FREEDOM -+-> INCLUDED ~ http://freedomincluded.com
        /|\      Free Software respecting hardware
_______________________________________________
Tech mailing list
[email protected]
https://lists.lopsa.org/cgi-bin/mailman/listinfo/tech
This list provided by the League of Professional System Administrators
 http://lopsa.org/

Reply via email to