Have you looked in the 2022 or 2025 edition to see if the wording changed?
  
  
  
  
Todd Williams     

  
Fire Protection Design/Consulting
  
Stonington, CT
  
860-608-4559
  
  
  
  
  

  
  
>   
> On Sep 24, 2026 at 10:45 AM,  <Joe Burtell [MT-BILL] 
> (mailto:[email protected])>  wrote:
>   
>   
>     
>  I've got a combined sprinkler/standpipe system I'm working through and want 
> to bounce a question off you, since you're on the NFPA 14 committee.
>   
>   
>   
>  THE SCENARIO
>   
>   
>   
>  I'm using NFPA 13 (2019) and NFPA 14 (2019). Facts:
>   
>   
>   
>  The FDC will be supplied with a pumper truck at 200 psi, as this is a manual 
> standpipe system.
>   
>  All pipe, fittings, and valves on the combined riser are rated 300 psi or 
> greater.
>   
>  The sprinklers are residential sprinklers, which only come rated to 175 psi 
> max — there's no higher-pressure listed option to spec around this.
>   
>   
>   
>  Since the riser is shared between the standpipe and sprinkler systems, I'm 
> trying to nail down whether that 200 psi FDC-boosted pressure is something 
> the sprinkler branch has to be designed/protected against, or whether it's 
> legitimately excluded from that side.
>   
>   
>   
>  THE DEFINITION CONFLICT
>   
>   
>   
>  NFPA 13 (2019), 3.3.235 - System Working Pressure:
>   
>  "The maximum anticipated static (nonflowing) or flowing pressure applied to 
> sprinkler system components exclusive of surge pressures and exclusive of 
> pressure from the fire department connection."
>   
>   
>   
>  NFPA 14 (2019), 3.3.24 - System Working Pressure:
>   
>  "The maximum anticipated static (nonflowing) or flowing pressure applied to 
> standpipe system components exclusive of surge pressures."
>   
>   
>   
>  NFPA 14's 2019 definition dropped the FDC exclusion that NFPA 13 still 
> carries. My understanding is the 2016 edition of NFPA 14 did exclude FDC 
> pressure, and the exclusion came back (worded differently, as an explicit 
> inclusion this time) in the 2024 rewrite. So in the 2019 pairing I'm stuck 
> with, NFPA 13 excludes FDC pressure from working pressure, and NFPA 14 
> doesn't carve it back out.
>   
>   
>   
>  WHY IT MATTERS HERE
>   
>   
>   
>  NFPA 13 also requires sprinkler components to be rated for at least 175 psi 
> or the max pressure they're actually exposed to, whichever is greater — 
> separate from how "system working pressure" is defined as a term. On a shared 
> riser, if the standpipe side gets boosted to 200 psi via the FDC, that 
> pressure is physically present at the riser regardless of which standard's 
> definition "counts" it.
>   
>   
>   
>  My residential sprinklers are only rated to 175 psi with no higher-rated 
> alternative. If any part of the sprinkler branch could see more than 175 psi 
> — even from FDC boost — that looks like a rating gap unless a PRV goes in on 
> the sprinkler side of the floor control assembly.
>   
>   
>   
>  WHAT I'D LOVE YOUR READ ON
>   
>   
>   
>  In the 2019 edition pairing, is FDC-boosted pressure meant to count as part 
> of the standpipe's "system working pressure," given NFPA 14 (2019) dropped 
> the exclusion language that NFPA 13 (still) has?
>   
>  For a combined system on a shared riser, does NFPA 13's exclusion of FDC 
> pressure actually relieve the sprinkler branch from needing protection 
> against it — or does the "rated for what it's exposed to" requirement 
> override that once the riser is shared?
>   
>  Practically: with 200 psi possible at the riser and 175 psi-max residential 
> sprinklers with no higher-rated option, is a PRV at the sprinkler takeoff 
> mandatory wherever calculated pressure (inclusive of anticipated FDC 
> contribution) could exceed 175 psi? Or is there some other intended mechanism 
> — FDC placard limits, a different assumption about how the two pressures 
> interact on a shared riser — that I'm missing?
>   
>   
>   
>  Any insight into the intent behind the 2019 language change, and how it's 
> supposed to interact with NFPA 13's exclusion in a combined system, would 
> really help.
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>  ​​​​
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>  Joe   Burtell
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>  Design   Manager
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
> D
>             
>   
>   
>   
>   
>   
> C
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>             
>   
>   
>   
>   
>   
>   
>                   
>   
>   
>   
>   
>   
>   
>   
>   
> 406-204-4653 (tel:406-204-4653)
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
> 406-861-4507 (tel:406-861-4507)
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>  3004   1st   Ave   South
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
> Billings
>   
>   
>   
>   
>   
>   
>   
>   
>   
>  ,   
>           
>   
>   
>   
>   
> MT
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   59101
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>  Office:   
>   
>   
>   
>   
>   
>   
>   
>   
>   
> 406‑247‑0470
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>  www.summitfiresecurity.com
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>   
>  This is a commercial email sent by Summit Companies or one of its 
> affiliates, with an office located at 1250 Northland Drive, Suite 200, 
> Mendota Heights, MN 55120. If you no longer wish to receive commercial emails 
> from Summit Companies, please let us know by contacting us by mail or by 
> email at privacy@summitcompanies to opt out.
>     
>  IMPORTANT: Information contained in this e-mail may be privileged, 
> confidential, and subject to other protections, including, but not limited 
> to, the Electronic Communications Privacy Act, 18 U.S.C. Sections 2510-2521. 
> If you are not the intended recipient, do not read, distribute, or reproduce 
> this transmission. If you have received this e-mail in error, please notify 
> the sender immediately and delete the message from your system. Thank you for 
> your cooperation.
>                                  
> _________________________________________________________ SprinklerForum 
> mailing list: 
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org 
> To unsubscribe send an email to [email protected]  
>           