Should be able to cover that with a "sprinkler design in racks independent from 
the ceiling" in the last few editions with ESFR sized in-rack heads.  It's the 
descendent of the FM 8-9 Scheme A that made its way into NFPA 13 and expanded 
over the last few years.  If you're working from a particular year NFPA I can 
send you a reference, in 2022 and 25 its near the end of the in rack design 
chapter.

Mike Morey
2025 NFSA Top Tech 
Champion<https://www.linkedin.com/posts/national-fire-sprinkler-association_congratulations-to-our-2025-top-tech-winner-activity-7326725245707431936-_5jg/>
 * NICET 
IV<https://credentials.nicet.org/47458792-752e-4926-86fc-bd4d47722218#acc.kBTieRXy>
 * 
CFPS<https://www.credly.com/badges/c05de73a-dbed-4c31-b1dc-0be93f3151f0/public_url>
Project Estimator * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625
email [email protected]<mailto:[email protected]>
24/7<outlook-data-detector://2/> SERVICE LINE 888.217.7055<tel:888.217.7055>
[cid:[email protected]]


From: James Crawford <[email protected]>
Sent: Wednesday, April 15, 2026 2:47 PM
To: '[email protected]' 
<[email protected]>
Subject: [Sprinklerforum] Exposed Expanded Group "A" Plastics

Looking for a protection scheme using in-rack sprinkler heads for exposed 
expanded Group "A" plastics but can't seem to find one. Building is 30' high, 
storage to 20' high on single row racks. Thank You James Crawford
ZjQcmQRYFpfptBannerStart
This Message Is From an Untrusted Sender
You have not previously corresponded with this sender.
ZjQcmQRYFpfptBannerEnd
Looking for a protection scheme using in-rack sprinkler heads for exposed 
expanded Group "A" plastics but can't seem to find one.

Building is 30' high, storage to 20' high on single row racks.

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email [email protected]<mailto:[email protected]>
Web: 
www.phaserfire.ca<https://urldefense.com/v3/__http:/www.phaserfire.ca__;!!FaxH778!ddi1z7RgfpeQfgl3n8l0OEjivNKeGVNwBlhqcJeYOPXRHhCUQfT3V2StETvi_bYQ1KkkvIWxyKU04-9tUz5Vl_c$>

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to