Call  R.T. Stearns in Portsmouth N.H.  603-319-4171.  They will absolutely 
know.  Tell them Wally sent you.  There will likely be a fee for call, but… 
They will know for sure.

From: Mike Watts <[email protected]>
Sent: Tuesday, May 20, 2025 1:59 PM
To: [email protected]
Subject: [Sprinklerforum] Diesel fire pump flow testing

External Email: ONLY open links/attachments from known safe sources
Ok this is a new one for me. Have a diesel driven fire pump that has a PLD 
pressure limiting driver. When it comes to the annual flow test, how do I test 
this properly per Nfpa? Would this be tested as a variable speed pump per nfpa?
I know on start up you disable the PLD to test and set relief valve pressure. 
On annual flow test the net pressure is low because RPMs are limited. Do I 
disable the PLD for the test to compare with pump data plate?  OR use RPM 
correction formula with PLD on? OR test as a variable speed pump? Sorry first 
PLD pump for me this is cool stuff just want to make sure I test it right. Not 
finding much info on PLD PUMPS 8n nfpa.

Ps called the manufacturer they could not help with annual testing requirements.

Mike Watts
Sprinkler Service Manager
Firetrol Protection Systems
4616 W. Howard Lane, Suite 700
Austin, TX. 78728
512-687-0115 Office
512‐660-4411 Cell
[email protected]<mailto:[email protected]>