I am looking at a job that shows a dry valve supplying Floor Control Assemblies 
with a standard detail. Including what appears to be the standard "paddle" type 
flow switch, along with an air vent.

Of course, that is not going to happen. Paddle switches being excluded for use 
in Dry. And the air vent SMH...

But it got me wondering.

How is everyone approaching this? When you have a dry valve, supplying Floor 
Control Assemblies?

The only Dry exception is 16.9.11.4 regarding parking garages.

All help appreciated.

R/
Matt


Matthew J. Willis, CWBSP, C.E.T.

Manager – Fire Design & Engineering

Ferguson Fire Design, LLC

[email protected]<mailto:[email protected]>