I have always treated auxiliary systems calcs the same as total area.

In other words, the total Sq FT of the Wet plus the Dry applies to the Wet 
system as the total building area protected by one system riser.

So to me, the hydraulics for the dry are treated like just another "Remote 
Area" in my mind.

For what it's worth, I treat the drains the same. In other words, the "Main" 
drain on the dry system, to me is a gravity drain, not needing to be routed 
anywhere for full flow.

That occurs where the water supply comes into the building in my mind.

R/
Matt


Matthew J. Willis, C.E.T.

Ferguson Fire Design, LLC

D: (602) 337-0721<tel:6023370721> C: (307) 236-8249<tel:3072368249>

[email protected]<mailto:[email protected]>



________________________________
From: Ben Young <[email protected]>
Sent: Tuesday, April 22, 2025 7:11 AM
To: 321 via Sprinklerforum <[email protected]>
Subject: [Sprinklerforum] BOR point for dry system

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
Let's say you have a remote dry system fed off a wet grid.

On your calc information box on the drawings and the actual hydraulic placard, 
do you put the demand at the base of the dry pipe valve riser, or do you put it 
at the base of the wet riser?

Obviously GPM would be the same, but pressure will be different.

I've been putting it at the base of the dry pipe valve riser myself, but was 
curious to see if this was in tune with the rest of the industry.

Thanks,


Benjamin Young