Assuming it's been filled with air already, yes.  A lot of places that use 
large quantities of the stuff store it un-filled where it is basically rolled 
up sheets of double layered non-expanded plastic. Then they run it through a 
machine that puffs air into it and heat seals one seam.  Once filled with air I 
can't see any way to not consider it expanded plastic as that is the nature of 
expanded plastic, entrapped air.

Mike Morey
CFPS 3229 * NICET S.E.T. 123677
Project Estimator * Fire Protection Group
Shambaugh & Son, LP an EMCOR Company
7614 Opportunity Drive * Fort Wayne, IN * 46825
direct 260.487.7824 /  cell 260.417.0625
email [email protected]<mailto:[email protected]>
24/7<outlook-data-detector://2/> SERVICE LINE 888.217.7055<tel:888.217.7055>
[cid:[email protected]]

From: James Crawford <[email protected]>
Sent: Tuesday, March 18, 2025 1:38 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Bubble Wrasp

We are looking at a project that has a large amount of bubble wrap to be stored 
on single and double row racks. Would this be an expanded Group A plastic due 
to the air bubbles? Thank You James Crawford Phaser Fire Protection Ltd. Phone 
604-888-0318
ZjQcmQRYFpfptBannerStart
This Message Is From an Untrusted Sender
You have not previously corresponded with this sender.
ZjQcmQRYFpfptBannerEnd
We are looking at a project that has a large amount of bubble wrap to be stored 
on single and double row racks.

Would this be an expanded Group A plastic due to the air bubbles?

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email [email protected]<mailto:[email protected]>
Web: 
www.phaserfire.ca<https://urldefense.com/v3/__http:/www.phaserfire.ca__;!!FaxH778!bsvAc8VIqSTod6cQjSgwoAVRGsRXm9D9DL6uActGmDnfcj0NFnaRim4IdVYO14BpxW-3zZ1dDKCqzDPe8Q3-eg4$>

This message is for the named person's use only.  It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission.  If you receive this message in 
error, please  immediately delete it and all copies of it from your system, 
destroy any hard copies of it and notify the sender.  You must not, directly or 
indirectly, use, disclose, distribute, print, or copy any part of this message 
if you are not the intended recipient.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to