We have seen multiple cases where the sub who was supposed to do the tenting
and insulating cut corners and the system froze. We won't bid for that method
anymore. MattSent from my T-Mobile 5G Device
-------- Original message --------From: Fpdcdesign <[email protected]> Date:
3/6/25 9:54 AM (GMT-06:00) To: Discussion list on issues relating to
automatic fire sprinklers <[email protected]> Subject:
[Sprinklerforum] Re: "Tenting" NFPA 13 (2019) Section 16.4.1.3. It references
insulated coverings as acceptable. I have seen several insulation applications
where chicken wire is used to hold the insulation in place. The box is kind of
overkill. Todd G Williams, PEFire Protection Design/ConsultingStonington,
CT860-535-2080 (ofc)860-554-7054 (fax)860-608-4559 (cell)On Mar 6, 2025 at
8:23 AM, <Chris Dorn> wrote:
<!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Aptos;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0in;
font-size:11.0pt;
font-family:"Aptos",sans-serif;
mso-ligatures:standardcontextual;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:#467886;
text-decoration:underline;}
span.EmailStyle19
{mso-style-type:personal-reply;
font-family:"Aptos",sans-serif;
color:windowtext;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;
mso-ligatures:none;}
@page WordSection1
{size:8.5in 11.0in;
margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
{page:WordSection1;}
-->
Yes, had an experience where the local building official required that the
piping be protected with tented insulation and then we had to build a plywood
box around the piping. I would have taken our objection to the State Fire
Marshall
and Building Officials, but the GC decided it was easier and quicker to just
do it at his cost. I tried to explain that they made servicing the sprinkler
system in the future way more difficult, but he just couldn’t get it. It was
infuriating and made worse
by the GC agreeing with the ridiculous requirement which only served to
embolden him.
Chris Dorn
From: Brian Harris <[email protected]>
Sent: Thursday, March 6, 2025 8:17 AM
To: [email protected]
Subject: [Sprinklerforum] "Tenting"
Anybody ever have an engineer reject plans saying “tenting” of insulation over
pipe is not acceptable?
Thank you,
Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com
Phone: 704.896.9989
Fax: 704.896.1935
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]