Thanks, found a section that shows them and they don't meet the 18"
rule. Will be adding sprinklers.
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
On 1/27/2025 5:00 PM, Brett Peters wrote:
Depends on the type of sprinklers above but typically if at least 18”
down from deflector and not over 48” then no.
On Mon, Jan 27, 2025 at 4:37 PM Bob Knight <[email protected]> wrote:
Would 48" wide lapendary panels require sprinklers?
The ceiling/roof above will be fully covered.
--
/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
Virus-free.www.avg.com
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
<#m_-4638697657746720064_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to
[email protected]
--
Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent From My iPhone
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]
--
This email has been checked for viruses by AVG antivirus software.
www.avg.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]