Thanks, found a section that shows them and they don't meet the 18" rule.  Will be adding sprinklers.

/Thank you,
Bob Knight, CET III//
/*/Fire by Knight, LLC/*/
//208-318-3057/
FIREBYKNIGHT


On 1/27/2025 5:00 PM, Brett Peters wrote:
Depends on the type of sprinklers above but typically if at least 18” down from deflector and not over 48” then no.

On Mon, Jan 27, 2025 at 4:37 PM Bob Knight <[email protected]> wrote:

    Would 48" wide lapendary panels require sprinklers?
    The ceiling/roof above will be fully covered.
--
    /Thank you,
    Bob Knight, CET III//
    /*/Fire by Knight, LLC/*/
    //208-318-3057/
    FIREBYKNIGHT

    
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
        Virus-free.www.avg.com
    
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>


    <#m_-4638697657746720064_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>

    _________________________________________________________
    SprinklerForum mailing list:
    https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
    To unsubscribe send an email to
    [email protected]

--
Thank You
Brett Peters
PFPS Ltd
(780) 777 0568
Sent From My iPhone

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email [email protected]


--
This email has been checked for viruses by AVG antivirus software.
www.avg.com
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to