States like NY State OPWDD have specific rules and do not allow 13D after a
multi fatal fire in Wells NY in 2009.

Was NOT a fire sprinkler issue but steps were taken to step up existing and
future group homes in NY State.

https://www.aclu.org/press-releases/grand-jury-report-wells-group-home-fire-presents-steps-nys-can-take-prevent-similar



Dominick Kasmauskas
Legislative Consultant
American Fire Sprinkler Association (AFSA)
518.937.4790
Kingsport, TN
www.FireSprinkler.org


On Wed, Jan 15, 2025 at 18:05 <[email protected]> wrote:

> Re: *NFPA 101 2018 Edition -*
>
>
>
> 32.2.1.1.1 Residential Board and Care – *Small Facilities* - limited to
> not more than sixteen (16) residents.
>
>
>
> 32.2.3.5.3.2 – Small Residential Board and Care Facilities can have an
> NFPA 13D system with the limitations that all habitable areas are
> sprinklered and if there are over eight (8) residents the water supply must
> be as for two-family dwellings plus some attic issues.
>
>
>
> No emergency power requirements.
>
>
>
>
>
> 32.3.1.1.1 Residential Board and Care – *Large Facilities* - more than
> sixteen (16) residents.
>
>
>
> 32.3.3.5.1 requires “full blown” NFPA 13 systems.
>
>
>
> Fire Pump as per NFPA 20 which only requires emergency power if a
> high-rise or power is not considered reliable.
>
>
>
>
>
> Re: *IBC 2021 Edition -*
>
>
>
> Deciding the occupancy classification is much more complicated…
>
> 1 – 5 occupants -
> R-3                                       NFPA 13D (903.2.8.1)
>
> 6 – 16 occupants -                          R-4, Condition 1
> NFPA 13D (903.2.8.2)
>
> R-4, Condition 2               NFPA 13R (903.2.8.3)
>
>                More than 16 occupants -            I-1, Condition
> 1                 NFPA 13R (903.2.6 Exception #1)
>
>
> I-1, Condition 2                 NFPA 13R (903.2.6 Exception #1)
>
>
>
> Use Conditions depend on the evacuation capability of the occupants which
> is way out of a sprinkler designer’s wheelhouse.
>
>
>
> Someone with knowledge of the facility needs to determine the Occupancy
> Classification.  A four-bedroom house converted to a Group Home with two
> occupants per bedroom is very likely to be a Group R-4, Condition 2
> occupancy which will require an NFPA 14R system with a UL Listed Fire Pump
> and an electrical supply that meets the requirements of NFPA 20.
>
>
>
>
>
> David L. Miller, P.E.
>
> *Engineered Fire Protection, **LLC*
>
> 11920 Richcroft Avenue
> <https://www.google.com/maps/search/11920+Richcroft+Avenue+Baton+Rouge,+Louisiana+70814?entry=gmail&source=g>
>
> Baton Rouge, Louisiana 70814
> <https://www.google.com/maps/search/11920+Richcroft+Avenue+Baton+Rouge,+Louisiana+70814?entry=gmail&source=g>
>
> 225-273-5040
>
>
>
> *From:* Mike Stewart <[email protected]>
> *Sent:* Wednesday, January 15, 2025 4:19 PM
> *To:* Discussion list on issues relating to automatic fire sprinklers <
> [email protected]>
> *Subject:* [Sprinklerforum] Re: 13D generator requirements
>
>
>
> From my experience Group homes should not fall under 13D. At the very
> least they are a 13R hazard. Even if they are in a standard home.
>
>
>
> Is there no engineer of record on this project? And why would a fire
> sprinkler designer be worried about a back up power source?
>
>
>
> Is there a permanent back up generator on site? If so did the salesperson
> who bid the project not exclude a transfer switch (being that it’s only a
> 13R system)?
>
>
>
> I have so many questions about this.
>
>
>
> Mike Stewart
>
> Dog Walker
>
>
>
> On Jan 15, 2025, at 8:44 AM, Urso, Paul <[email protected]>
> wrote:
>
> 
>
> I would assume if it is a state funded group home that a generator will be
> installed.
>
> It is not code for the sprinkler system itself.
>
>
>
>
>
> Paul J. Urso
>
> Designer/Engineering Coordinator
>
> 9 Sullivan Road Holyoke, MA 01040
> <https://www.google.com/maps/search/9+Sullivan+Road+Holyoke,+MA+01040?entry=gmail&source=g>
>
> M: 860-883-6282 E: [email protected]
>
>
>
>
>
> 
>
> <Outlook-qzwuc4tu.png>
>
>
>
>
>
> © 2023 Everon. All rights reserved. The information contained in this
> transmission is confidential and/or may contain attorney-client privileged
> communications intended for the use of the individual or entity named
> above. If the reader of this electronic message is not the intended
> recipient, or the employee or agent responsible to deliver it to the
> intended recipient, you are hereby notified that any dissemination,
> distribution or copying is strictly prohibited. Everon and its parent,
> affiliates, and subsidiaries reserve the right to monitor communications
> handled by its data communications systems to help ensure compliance with
> Everon's policies, confidentiality obligations, and applicable laws.
> Licenses held under Everon available at www.everonsolutions.com
>
>
> ------------------------------
>
> *From:* Fpdcdesign <[email protected]>
> *Sent:* Wednesday, January 15, 2025 7:45 AM
> *To:* Sprinklerforum <[email protected]>
> *Subject:* [Sprinklerforum] 13D generator requirements
>
>
>
> I am working on a group home, which by all of the Code analysis, requires
> a standard 13D system. They propose to install a pump and tank system.
> Would a back up power supply be required for this? I have never been asked
> about it but can’t find much that addresses it.
>
>
>
> Todd G Williams, PE
>
> Fire Protection Design/Consulting
>
> Stonington, CT
>
> 860-535-2080 (ofc)
>
> 860-554-7054  (fax)
>
> 860-608-4559 (cell)
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
>
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
> Virus-free.www.avast.com
> <https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
> <#m_7131047715055378835_DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to