For a 13D, I do not think so. I believe NFPA 20 does not come into play until a 13R, or 13.
The main point of the 13D is supposed to be lower costs. A group home sounds like at least an R system.. But you have the full story so will defer to your analysis. R/ Matt Matthew J. Willis, C.E.T. Ferguson Fire Design, LLC D: (602) 337-0721<(602)%20337-0721> C: (307) 236-8249<(307)%20236-8249> [email protected]<mailto:[email protected]> ________________________________ From: Fpdcdesign <[email protected]> Sent: Wednesday, January 15, 2025 7:45 AM To: Sprinklerforum <[email protected]> Subject: [Sprinklerforum] 13D generator requirements Caution: This email originated from outside of the organization. DO NOT click links or open attachments unless you recognize and trust the sender. ________________________________ I am working on a group home, which by all of the Code analysis, requires a standard 13D system. They propose to install a pump and tank system. Would a back up power supply be required for this? I have never been asked about it but can’t find much that addresses it. Todd G Williams, PE Fire Protection Design/Consulting Stonington, CT 860-535-2080<tel:860-535-2080> (ofc) 860-554-7054<tel:860-554-7054> (fax) 860-608-4559<tel:860-608-4559> (cell)