Broken hangers you're looking for. Painted sprinklers you're looking for. Leaking pipes you're looking for. Essentially, you're just looking for what 25 says to look for and only what you can see from the floor. As soon as you question the layout or the design criteria, you have stepped outside your certified area of expertise and have taken on the role of layout technician and/or PE. At that point, you might as well question whether the structure is adequate to support the system, whether it can tolerate a likely seismic event, or if the building itself can withstand the impact of a fully fueled 767 crashing into it. And what about that unsprinklered munitions factory? What's up with that?
On Fri, Dec 20, 2024 at 11:42 AM Bob Caputo <[email protected]> wrote: > Read section 1.1.3 of NFPA 25. You’re inspecting what is there for wear > and tear purposes. You are not verifying the design or installation of any > system > > > Bob Caputo, CFPS > *President* > > *American Fire Sprinkler Association* > p: 214-349-5965 ext124 > w: firesprinkler.org > <https://www.facebook.com/firesprinkler.org/> > <https://twitter.com/afsa/status/1039528345367732224> > <https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/> > <https://www.instagram.com/firesprinklerorg/> > > *Train a safer, more efficient workforce.* > > By enrolling your employees in the AFSA Apprenticeship Training Series > for Sprinkler Fitters > <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149>, > you will reap the benefits of a qualified, professional installation crew. > Well-trained employees will work smarter, increasing your company's > productivity and, in turn, its profits. Learn more > <https://www.firesprinkler.org/WWW/Education/Apprentice_Training/WWW/Education/Apprenticeship_Training.aspx?hkey=e88ef09e-d74c-407f-abcd-995aff866149> > . > > > On Fri, Dec 20, 2024 at 10:35 AM Brandon Bridgford <[email protected]> > wrote: > >> How do you approach unprotected areas in regards to ITM and NFPA 25. I >> know there was a discussion in the past regarding inspecting a system as >> is, rather than writing up deficiencies that have to do with system design. >> I have been told that this can open up more liability if you are not >> inspecting all design elements (i.e. density, hazard levels, etc.) >> >> >> >> Thank you! >> >> Brandon >> >> >> >> >> >> >> >> _________________________________________________________ >> SprinklerForum mailing list: >> >> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org >> To unsubscribe send an email to >> [email protected] > > > _________________________________________________________ > SprinklerForum mailing list: > https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org > To unsubscribe send an email to > [email protected]
_________________________________________________________ SprinklerForum mailing list: https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org To unsubscribe send an email to [email protected]