If the overall width from outside of left row of tires to outside of right row 
of tires is 6' or less, is this a single-row rack or a double-row rack?
Reference NFPA 13 (2019) sections 3.3.56 and 3.3.191.


[cid:[email protected]]
Thanks,
Ed


[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]

[cid:[email protected]]


Ed Kramer
Design Manager | Bamford Fire Sprinkler Co., Inc.
P:    913.432.6688
F:    913.432.5294
M:   785.766.4894
A:   5134 Merriam Dr.  Shawnee Mission KS  66203


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to