You don’t say how tall the building is?  or how high the storage is in the 
racks?.
I assume you are using the NFPA 13 requirement for exposed expanded plastics up 
to 35' high in a 40' building, = K25.2 @ 60 psi.
But is under 30ft roof height then you can store to 25' and K25.2 @ 30 Psi..

You may also want to look into putting a combination of roof sprinklers and 
in-rack sprinklers to accomplish this.

Are there smoke and heat vents in the building? If so and a roof height of 27' 
or lower, you could do the special design of .60/2000 with standard heads.

Have a good day.

Anthony Carrizosa 
Project Manager | Fire Protection 
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593 
 




-----Original Message-----
From: Gerzayn Fuentes @ KOLTEK.MX <[email protected]> 
Sent: Friday, July 19, 2024 12:59 PM
To: [email protected]
Cc: Francisco Reveles @ Koltek.mx <[email protected]>
Subject: [Sprinklerforum] UUP / Plastics A unexpanded exposed

Hello everyone!

We are designing an expansion project for an Plastic A Unexpanded Exposed or 
UUP with racks warehouse. Design specification is 12K25.2 @
60 psi + 250 gpm x 60 minutes. The existing pump is 2,000 gpm @ 120 psi, and an 
existing underground schedule 40 steel network is more than 10 years old. We 
are using a factor C=100.

The above gives us 4" branch lines, 8" mains and a 10" riser, using 3 mains and 
it gives us the curve, but we need to lower the pipe diameters. We have never 
seen a 10" riser. We know that the problem lies in the capacity of the fire 
pump, and the client wants to save as much as possible and reduce the risk due 
to the structural load.

Our question is, can we have a grid sprinkler system with 2 risers of 8" that 
feed it? We can't find anything in NFPA or FM Global standards that prevents 
this, but at the same time I've never seen a system like this installed.

Greetings and we look forward to comments.
-- 

Gerzayn Fuentes Campos / director general [email protected] México.
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fwww.koltek.mx&c=E,1,u3yw4iqvZc_1R6_UWJmuBdWsV6MnSWXOqOd0EEoIvs-tDebRPmP3xnGEsvsMkLYHiZXHFGsWbGHRPCQyHx1y67ATpq-4F49u3rNzwtz3DWar&typo=1

--
 
<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2fexpofire.ownersys.com%2fregistro&c=E,1,9qXb9Qr5L8FdXHQMZI2hhLg-cV7GjUj5u93If2Wo-5usoFaBGHHCbzu7IJxpJTEy7JChz5WmaNePxybdhDLWbjL7e9PIijjJkSZN5OkQviefwmwWt0hC_kmRdw,,&typo=1>

_________________________________________________________
SprinklerForum mailing list:
https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,aqYFXpmPtEZ-GawQ2h5x7go6LRER_vjLLMJtbNRdPYbGVwu0JRqbDrcYZ0pu3YMuUKpiiF3jyqmBIYpKUEX5DEAf6RtePCPcawVeje8dUinrZHhfywMPPLxNC0k,&typo=1
To unsubscribe send an email to [email protected]

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to