Depends on which version you are using.  '16 and '19 only refers to storage 
needing to be 18" or more, not shelving specifically.

11.3.7.1.2  NFPA 13 - Standard for the Installation of Sprinkler Systems (2022)

Shelving, and any storage thereon, directly below the sprinklers shall not 
extend above a plane located 18 in. (450 mm) below the ceiling sprinkler 
deflectors.


Thomas R. Worley
  Estimator/Design Manager
  Fire Foe Corp.
  999 Trumbull Ave.
  Girard, OH 44420
  P: 330-759-9834 x112
  F: 330-759-8949
  E: [email protected]<mailto:[email protected]>
[cid:[email protected]]<http://www.firefoe.com/>

From: Fpdcdesign <[email protected]>
Sent: Wednesday, May 15, 2024 2:11 PM
To: Sprinklerforum <[email protected]>
Subject: [Sprinklerforum] Obstruction below sidewall sprinkler

I am working on a system with extended coverage sidewall sprinklers, allegedly 
protecting an LH occupancy. The space is a high ceiling area where the 
elevation distance between the high and low ceilings is 22". The low ceiling is 
protected by pendants.

4" below the center line of the sidewall sprinklers is a shelf that stick out 
6" (4-1/4" from deflector to the edge). It would seem to me that this is an 
obstruction but it is not addressed in 13. Any thoughts?