Can a sprinkler deflector be level with the bottom of an obstruction at 6" 
away? NFPA-13 (2022) Table 10.2.7.2 (a) says you can be 0" above the bottom at 
less than 1' away. I have in rack sprinklers and the contractor put the pallet 
stops above the tier being protected (wrong tier).
Thanks,George Medina Jr.
Sr. Fire Sprinkler DesignerSINGLETON FIRE PROTECTION INC.Office: (818) 
252-5744Cell: (323) 906-5701
Business Hours: 9:00am-5:00pm
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to