Yessir! That’s exactly what happened. Snoots are being installed as we speak. 
Thank you!

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: [email protected] <[email protected]>
Sent: Friday, April 19, 2024 8:32 AM
To: [email protected]
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Back Feeding Through the FDC?

If you did not put in “check snoots’, or check valves behind each in this 
configuration, then the water is circulating back thru these to the truck.

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Manager – Southwest Region
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<http://www.fergusonfire.com/>


From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Friday, April 19, 2024 4:57 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Back Feeding Through the FDC?

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
Don-
The truck is hooked up to a private hydrant downstream of the BFP and located 
next to the yard FDC. The FDC is on a dedicated line back to the building, 
tying in downstream of the pump discharge.

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: Don Casey <[email protected]<mailto:[email protected]>>
Sent: Thursday, April 18, 2024 7:45 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: [EXTERNAL] Re: Back Feeding Through the FDC?

Where are they drawing the water from?


On Apr 18, 2024, at 6:30 PM, AKS-Gmail-IMAP 
<[email protected]<mailto:[email protected]>> wrote:

________________________________
[CAUTION: This email originated from outside of the organization. Do not click 
links or open attachments unless you recognize the sender and know the content 
is safe.]
________________________________
I have an odd request. How about you taking some time to describe exactly what 
you are referring to so that we do not have to guess every aspect. Assume you 
have told us next to nothing so far.

Thank you.

Allan Seidel
St. Louis, MO

On Apr 18, 2024, at 3:46 PM, 
[email protected]<mailto:[email protected]> wrote:

AHJ had us remove a 5” Storz and replace it with a custom header that has (4) 
2-1/2” hose valves for the FDC. Standpipe test has failed 3 times and now 
they’re thinking water is circulating through these valves back to the fire 
truck. Anybody ever run into something like that?

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,QdrGtBJFnnMBq_MxxAdgeDYtz-kB_ImE1v644LM95k3pSsbZhpAHkfzIxbBAEvQOzAsUrBdDYj-raGtp4ztl31D075dEqruopd_bL_eyWLv3BqFlGtN8gw,,&typo=1>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,F04Y1ZsNJgEjoZu26JrpArvpNnpn1VQia8Y3DEJHhsrTlB4WnFHgA8B3i090VyRlIGM0B5CwQ8xn5n1odIP1gauEpZQcxaN4zdCw95t6VA,,&typo=1&ancr_add=1>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to