A separate ”riser/backflow room” that has a door opening onto the stair 
enclosure (even a rated door) could be problematic per the building code.

2018 IBC 1023.4 limits the types of spaces that can open directly to interior 
exit stairways.

From: å... .... <[email protected]>
Sent: Tuesday, March 26, 2024 7:31 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Riser in a rated stair enclosure

---- SCDLLR NOTICE (M365) ----

•  This email is from an external email address. Please use caution when 
deciding whether to open any attachments or when clicking links.
•  Personally Identifiable Information (PII) should not be included in e-mail 
text or attachments. Do not save or transmit PII unencrypted.
Rated chase for sprinkler piping and/or riser appurtenances within a rated 
stairway is excessive protection per past norms of practice.
I would tolerate sprinkler pipe and appurtenances in a stairway, provided 
egress AND maintenance clearances.
Risk tolerance has declined over the years, but this ask might originate from 
motivations that have not delinced over the years.

Scot Deal
Excelsior Risk & Fire Engineering
gms:  +420 606 872 129


The meaning of life is to find your gift.  The purpose of life is to give it 
away - picasso



On Tue, Mar 26, 2024 at 3:48 PM Hinson, Ryan 
<[email protected]<mailto:[email protected]>> wrote:
Placement/coordination within the stairwell is also important since the riser 
location cannot encroach into the minimum egress width or height required 
through the stairwell.

Ryan L. Hinson, PE*, SET**  \  Burns & McDonnell
Associate Fire Protection Engineer \ Upper Midwest Region
O 612-900-3755 \  M 763-688-4045 \  F 952-229-2923
[email protected]<mailto:[email protected]>  \  
burnsmcd.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.burnsmcd.com%2f&c=E,1,Mcj_Al8hjmfFBEV5_U05JpEBZ_o27vDB6iurmR9u1bDX6w4DxY5YBgDW0njpL0u8nOdkqZsMaWWArBUcPbYJMog3HfySg-yrzv-kQ-q7HKXsdKFMQw,,&typo=1>
8201 Norman Center Drive, Suite 500  \  Bloomington, MN 55437
*Registered in: AK, LA, MD, MN, PA, TX, & UT
**NICET IV - Water-Based Systems Layout

From: Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, March 26, 2024 3:57 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Riser in a rated stair enclosure

Of a separate riser ROOM for backflow, etc.   Definitely not saying that you 
need a chase within the stair shaft, just that you’re not allowed to use the 
under-landing space for a “riser room”.

Steve

From: Prahl, Craig <[email protected]<mailto:[email protected]>>
Sent: Tuesday, March 26, 2024 1:48 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Riser in a rated stair enclosure

I’ve never seen a requirement for a 1 or 2-hr enclosure of a riser in a stair.  
The stair towers I’ve encountered are typically rated 2-hrs and the combination 
sprinkler/standpipe riser located under the first landing or off to the unused 
side of the ground level has never been rejected by an AHJ.

Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Steve Leyton 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, March 26, 2024 4:30 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [EXTERNAL] [Sprinklerforum] Re: Riser in a rated stair enclosure

Right, as long as your “riser/backflow room” is separated from the rest of the 
stair shaft.   And it might have to be 2-hour rated, not just 1-hour.

To the question of the sprinkler riser, there isn’t any restriction in the 
code, except for the obvious provisions for fire-stopping penetrations.

Steve L.

From: Anthony Carrizosa 
<[email protected]<mailto:[email protected]>>
Sent: Tuesday, March 26, 2024 1:22 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Riser in a rated stair enclosure

We do backflows and risers in stairs all the time, typically below the 
intermediate landing, as long as it’s a minimum 1 hour construction then it has 
been ok with most jurisdictions. Remember standpipes and floor controls are 
typically in stairs as a standard.

Anthony Carrizosa
Project Manager | Fire Protection
7855 S 206th St Kent, WA 98032
Cell: 206-679-5283 | Office Dir: 253-341-4593
[cid:[email protected]]
https://archerconstruction.com<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2farcherconstruction.com*2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1__;JSUlJQ!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tHph3goA$>

From: Jeff Werre <[email protected]<mailto:[email protected]>>
Sent: Tuesday, March 26, 2024 1:09 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Riser in a rated stair enclosure

Does code allow a sprinkler riser to be installed in a rated stairwell?

I cannot find anything that prohibits it, but would like others opinions 
(experiences).

Thank you-

Jeff Werre, CFM
Fire Plan Review and Inspection Specialist

Development Services
City of Goodyear, Arizona
1900 North Civic Square
Goodyear, AZ 85395

c 602 316-0704
 w 
goodyearaz.gov<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.goodyearaz.gov*2f&c=E,1,HWheNqpd4bMAObWDA1Pz4jKGCAJR-thfNkyG-V6ubIPnRmE78JXq5nU1kLB5Uv0b6yAs3DnR0fq9Cb648VwhZkjzd0drubjF-G192TGVad51Zbnsm7L6vOrmJg,,&typo=1__;JSUlJQ!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tVFDFq8g$>
e [email protected]<mailto:[email protected]>





From: Ken Wagoner 
<[email protected]<mailto:[email protected]>>
Sent: Wednesday, February 21, 2024 1:17 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Re: NFPA 14 2019 Hose Connection on the Roof

⚠ This email arrived from an external source - Please exercise caution when 
opening any attachments or clicking on links

Completely agree with you John.

Considering that I work with two adjacent agencies, each of which uses a 
different hose thread.  One uses National Standard Thread, the other National 
Hose Thread.  It's difficult to explain to contractors that identification of 
the hose threads to be supplied on private fire hydrants or hose valves can be 
as critical as it gets.

sincerely,
Ken Wagoner, SET
Parsley Consulting
500 West Mechanic Street
Harrisonville, Missouri 64701-2235
Phone: (760) 745-6181
Visit the 
website<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.parsleyconsulting.com*2f&c=E,1,Y5zKJKPEh1mBEBqSR-VE9cUKl5y-eyP8BpvmE_5j9ZqW2eJbNphYzrCMBZ-2YuX6d-RRkHI4gQ1FV-cvOeCfRC58uZS9NiToZv2mx7909oCqLvCW_n5hDHeK&typo=1__;JSUlJQ!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tX2yXVSk$>


On 2/21/2024 1:13 PM, John Denhardt wrote:
Rick’s and Steve’s comments are spot on. Give the fire department what they 
need/want. Do not install something that no one will ever use in an emergency 
condition.

John
John August Denhardt, P.E.
Vice-President Engineering and Technical Services
American Fire Sprinkler Association
301-343-1457

On Feb 21, 2024, at 13:30, Rick Matsuda 
<[email protected]><mailto:[email protected]> wrote:

Steve’s guidance is the best.
When it comes to hose valves and standpipe requirements, always verify with the 
AHJ to find out what they want.
Rick

On Feb 21, 2024, at 12:09 PM, Steve Leyton 
<[email protected]><mailto:[email protected]> wrote:

To Rick’s comments:

Concur, and also offer that while the standard doesn’t require a valve where 
there is no roof access, I am aware of numerous AHJ’s who do.   The stated 
intent of the rooftop connection(s) is to enable forward flow testing of the 
system.   However – and this goes to my mantra of many years now – it is 
incumbent on the designer to verify with the serving FD is they require roof 
connections that they may use for firefighting.   I have been made aware of 
several fire incidents that used roof connection hose streams  and I am also 
aware of fireground strategies that encompass these connections.

The foregoing is my opinion only and does not represent NFPA or the NFPA 14 
Technical Committee, nor intended to serve as an interpretation of the standard.

Steve L.



From: Rick Matsuda <[email protected]><mailto:[email protected]>
Sent: Wednesday, February 21, 2024 9:51 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]><mailto:[email protected]>
Subject: [Sprinklerforum] Re: NFPA 14 2019 Hose Connection on the Roof

This is my opinion only from what I remember after being retired for ten years.

The requirement for installing a hose valve is driven by the stairway 
requirements found in the building code which requires at least one stairway 
providing access to the roof.

If the stairway extends to the roof, then a hose valve is required at the top 
landing or on the roof.

If there is no roof access from the stairway, then no hose valve is required.

The fire service will use the hose valve where they have safe access from the 
stairway but they will not walk across the roof dragging fire hose to hook up 
to a hose valve located where no safe access was provided.
Rick Matsuda

On Feb 21, 2024, at 10:47 AM, Fpdcdesign 
<[email protected]<mailto:[email protected]>> wrote:

There are people here with more experience than I,  but if one outlet goes to 
the roof, the requirement is met.


On Feb 21, 2024 at 11:34 AM, <Joe Burtell 
[MT-BILL]<mailto:[email protected]>> wrote:

If I have 3 stair towers and the middle on has access to the roof and I provide 
a connection as required by 7.3.2.7* “Hose connections shall be provided at the 
highest landing of stairways with stairway access to a roof”, do the other (2) 
not have to go to the roof because of 7.3.2.9.2 “The hose connection required 
by 7.3.2.9 shall not be required where at least one hose connection in 
accordance with 7.3.2.7 is provided in the building”.

<image001.jpg>
Joe

Burtell
Fire Sprinkler Manager
D
C


406-204-4653<tel:406-204-4653>
406-861-4507<tel:406-861-4507>
3004 1st Ave South
Billings
,
MT
 59101
Office:
406‑652‑7697
www.summitfiresecurity.com<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=http*3a*2f*2fwww.summitfiresecurity.com*2f&c=E,1,ZyzzqWo58xliyC5jRd9RdTLBBZo5jBEbiHix11FarpdW6p9BZLi5cyYnCyfcGhCFs7Mjew4A84L4gMd9Zn-QcKk5wbpkUpp2_prGEtUdqFeTwliA1vO3eEu-2E71&typo=1__;JSUlJQ!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tjGXKPfo$>
This information transmitted, including attachments, is intended only for the 
person(s) or entity to which it is addressed and may contain confidential 
and/or privileged material. Any review, retransmission, dissemination or other 
use of, or taking of any action in reliance upon this information by persons or 
entities other than the intended recipient is prohibited. If you received this 
in error, please contact the sender and destroy any copies of this information.
_________________________________________________________ SprinklerForum 
mailing list: 
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,zSczA6fh1z_DZmRiDK-SmOo2Q4iD1ybs-dofDAvbol2ARplwrC3CBPuJ5a3M1J8_FALzCrYwXVIdMdoRY1GetEF5HPRcSwVLnkfeGB7fJAT0jA,,&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tFELFh_8$>
 To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
<image001.jpg>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,cn2QOu3An6_NJyh_-n31_xLLKLAryTT4kv8MVY8TqJ2tAbIic9WRP3VMiL7Zsa_JQjzaIzYp9C1xb376t1oQxX-odSiNENfy2M5txOLU23NwBAyI53R1EyIXksgS&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tXyO6WrE$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,Gi862oLoF3I3PplbXyhBlyIqWk1hlUfaFq9LFqSSetXU_-QR2vszIPHoPCLemLpvP0IDslPxYZ0DJomXGuGZ1wGFfIq8RBojUhao19aiCM1LBGtLKy2trXyxLJY,&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3tEoX6sD4$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,MWR4WxvMm_voDTNku1D03F-6A9h7Gjbw2wvOS49dDZ4dGxceCjdtDa2_nTMSn1oskjiBgoFgJqtSxtjY9p-j1EVkWm8Y_tlvE_y1U995rCMZ_84,&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3twlbc8x8$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>




_________________________________________________________

SprinklerForum mailing list:

https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/linkprotect.cudasvc.com/url?a=https*3a*2f*2flists.firesprinkler.org*2flist*2fsprinklerforum.lists.firesprinkler.org&c=E,1,Zpm0EABfFsWYaANMGgf1uWLhtVfyI7HnZMUfAbuYLjv9MsLHX1mMcjxoSR48b1-eE-_y1osOjMNHzemMmoczBd_hkPjZgDRcLqK2w6x0YKgX&typo=1__;JSUlJSU!!B5cixuoO7ltTeg!AKDEQrf6NuN-W7D9y4dezAtAkbuSU8nl5s0ZAFQ7pDJyr1jiHYyoFHcF4_6Yz8odTqlPaH82RnQG9j3ttg6vig4$>

To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

All messages created in this system belong to the City of Goodyear and should 
be considered a public record subject to disclosure under Arizona Public 
Records Law (A.R.S. 39-121). City employees, City public officials, and those 
who generate E-mail to them, should have no expectation of privacy related to 
the use of this technology. If you are not the intended recipient you are 
notified that disclosing, copying, distributing or taking any action in 
reliance on the contents of this information is strictly prohibited.

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,P1fvRWnKNzpfsidNqQvsyxNPpRggqRYm7M4P7LcUqziXMTxQCOPSmwfl_Q4uI0PmX679d-sJ9yF6pMrZZCQYAuUtHo_i2iTo4jlD2wYzvQ,,&typo=1>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to