Suction control goes after the pump, before the check.   Has a sensing line to 
the gate valve before the pump that controls it. We use ClaVal

On Apr 12, 2024 12:12 PM, [email protected] wrote:
I have to put a suction control valve on a fire pump for the first time. I’m 
assuming it goes on the suction side of the pump. Does it go before or after 
the RPZ backflow? Anyone have any preferences as to brand or model; this one is 
an 8”. First time in 45 years of doing this.