A lot depends on the year of the standard being applied, but YES an AHJ can
(and should) require things that make sense for his/her community and the
methods used or planned for fire and EMS responses.  In this case, you are
on solid footing because NFPA 13 (2019 edition) section 16.9.11.1 requires
floor control valves in multistory buildings exceeding two stories in
height.

 

This requirement was added to NFPA 13 in the 2013 edition (section 8.16.1.5)


 

 

 

 


  <https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1> 


Bob Caputo, CFPS


President


American Fire Sprinkler Association

c:     760-908-7753


p:

214-349-5965 ext124 


w:

 <http://firesprinkler.org/> firesprinkler.org  


 <https://www.facebook.com/firesprinkler.org/>
<https://twitter.com/afsa/status/1039528345367732224>
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/
>    <https://www.instagram.com/firesprinklerorg/> 

 

Top-Notch Training for ITM Technicians!

AFSA has taken ITM) training to the next level with three new courses:
<https://www.firesprinkler.org/programs/beginning-itm-workshop/> Beginning
ITM,  <https://www.firesprinkler.org/programs/intermediate-itm-workshop/>
Intermediate ITM, and
<https://www.firesprinkler.org/programs/fire-pump-itm-workshop/> Fire Pump
ITM. Each workshop offers CEUs, CPDs, and contact hours. Expand your
business and increase your employees' knowledge and skill set with these
training opportunities!

 

From: [email protected] <[email protected]> 
Sent: Tuesday, April 9, 2024 6:57 AM
To: [email protected]
Subject: [Sprinklerforum] Floor Control Valves

 

I have a 3 story older building being renovated with sprinkler system being
added. My question is can AHJ require a floor control valve to be added to
each floor. Plans only show 1 floor control valve for the first floor. 1st
floor being business, 2nd and 3rd floor being residential and attic space
being sprinklered also. Concern of freeze and break in attic on older
building and to be able to isolate a floor after a fire. 

 

Thanks 

Chris Jones, Fire Marshal

Urbana Fire Division 