So, to get into greater detail, Ammonium Nitrate by itself is a class 2 
oxidizer.  Only when they come in contact with organic materials can they start 
a fire.   Otherwise, it is not a flammable or combustible.  It accelerates 
burning and under specific conditions can create an explosion when combined 
with other agents.

Diesel fuel is either a class IIIA or II depending on the additives.  Verify 
via SDS.

Quantities of materials come into play when if comes to the occupancy 
classification of the space.  More than 250 gallons of ammonium nitrate in a 
non-sprinklered area and you’re into a H-3 occupancy.  H3 will require 
sprinkler protection as well as secondary containment for liquid spill and 
sprinkler discharge.

Diesel fuel if Class II or IIIA will also have limits and could push the space 
into a H3 occupancy.

However, this one gets a bit tricky as some might argue that in a mine the 
building code doesn’t apply since there is no building.  This becomes a 
conversation with the owner and the responding fire department as to how the 
area should be addressed from a code perspective.  The local building code 
official might not even have any jurisdiction over this operation.


Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Ron Greenman <[email protected]>
Sent: Saturday, April 6, 2024 7:04 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Re: Protecting underground storage of 
explosives.

https://codes.iccsafe.org/content/IFC2018/CHAPTER-56-EXPLOSIVES-AND-FIREWORKS?site_type=public<https://urldefense.com/v3/__https:/codes.iccsafe.org/content/IFC2018/CHAPTER-56-EXPLOSIVES-AND-FIREWORKS?site_type=public__;!!B5cixuoO7ltTeg!HcoNsBHu1Kt7gDx9eIsIlgC7kQ0B1QsdtYW10ciYB40ZfDiIEMRpBgT8My0j_cMinCaHcEjjLt41ThaNNxWE-ws$>

On Sat, Apr 6, 2024 at 1:20 PM Prahl, Craig 
<[email protected]<mailto:[email protected]>> wrote:
Munitions and explosives are typically protected via separation.  On military 
projects, storage areas such as these are either semi-subterranean (partially 
earthen covered bunker), or just physically separated from other structures by 
several hundred feet.

I do hope the components are adequately separated.

Fire is usually not an issue in these spaces since there should be very 
stringent controls on ignition sources.  So, we don’t waste money on sprinklers 
or other types of suppression systems.  They just aren’t going to stop an 
explosion event.  Once it’s done, it’s done.

You can take a look at UFC 4-420-01, May 2015 for the way munitions and 
explosive storage is handled by the military.  UFC = Unified Facilities 
Criteria.  You can search for it on-line.  There are no restrictions for access.

You’d also have to  deal with sprinkler run-off and being underground, that 
might be a big challenge.

So, basically, this isn’t a sprinkler contractor project.

Craig Prahl | Jacobs | Fire Protection SME – Special Hazards | 
[email protected]<mailto:[email protected]> | 
www.jacobs.com<https://urldefense.com/v3/__http:/www.jacobs.com/__;!!KZTdOCjhgt4hgw!-_khxU8gU0_6jc895I7kRbnU8JghRDsWgqOblZ4jr7Qp2IVbR30VYw_hWvNFtphnl0uWpB9KIvbYi1pvZz4$>
1041 East Butler Road   Greenville, South Carolina  29606
CONTACT BY: Phone 1-864-676-5252, Email or MS TEAMS


From: Chris Dorn 
<[email protected]<mailto:[email protected]>>
Sent: Friday, April 5, 2024 4:05 PM
To: 
[email protected]<mailto:[email protected]>
Subject: [EXTERNAL] [Sprinklerforum] Protecting underground storage of 
explosives.

Trying to help a friend of a friend. Has anyone ever provided any type of fire 
suppression system for underground storage of ANFO (Ammoniun Nitrate and fuel 
oil mixture)? The area in question is in a limestone mine underground. The 
space is pretty large and has 30’ ceilings so I’m guessing that chemical 
suppression is not going to be an option. I tend to believe that sprinklers may 
not be the route to go. Water will apparently render the ANFO inert but in case 
of a fire I’m not sure that the sprinklers could operate fast enough to provide 
any real protection. Additionally, the water supply is inadequate for almost 
any type of sprinkler system anyway.

I’m not really finding much in NFPA except Annex C in NFPA 495 which refers to 
separation distances. I did find a reference to NFPA 490 2002 Edition but 
cannot find a current code so I’m guessing it was folded into 495 at some point.

Any direction at all would be appreciated to help me in my research.

Chris Dorn
Dorn Fire Protection LLC


________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://urldefense.com/v3/__https:/lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org__;!!B5cixuoO7ltTeg!HcoNsBHu1Kt7gDx9eIsIlgC7kQ0B1QsdtYW10ciYB40ZfDiIEMRpBgT8My0j_cMinCaHcEjjLt41ThaNURUcXac$>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

________________________________

NOTICE - This communication may contain confidential and privileged information 
that is for the sole use of the intended recipient. Any viewing, copying or 
distribution of, or reliance on this message by unintended recipients is 
strictly prohibited. If you have received this message in error, please notify 
us immediately by replying to the message and deleting it from your computer.
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to