I am looking at Figure 25.3.2.4.1 (e) In Rack Sprinkler Arrangement and Design, 
Exposed Nonexpanded Group A Plastic Commodities Up to 25 ft. in Height in Up to 
a 35 ft, High Building.
Option 2: .30 over 2,000 sq. ft. Notes (1) In-rack sprinklers are 
ordinary-temperature-rated, quick - or standard-response, pendant or upright, 
minimum K-5.6 (K-80), and designed for a minimum of 14 in rack sprinklers 
(seven in rack sprinklers on each level) operating at 30 gpm (114 L/min) when 
one level of in rack sprinklers is installed.
Is this a typo? am I not understanding it correctly? Should it say 'when two 
levels of in rack sprinklers is installed.' or Should the GPM be different with 
two levels? Option number 1 is pretty straight forward -

Option 1: .80/1,500 sq. ft. Notes (1) In-rack sprinklers are 
ordinary-temperature-rated, quick - or standard-response, pendant or upright, 
minimum K-5.6 (K-80), and designed for a minimum of 8 in rack sprinklers 
operating at 30 gpm (114 L/min) when one level of in rack sprinklers is 
installed.

Thanks for any clarity,George Medina Jr.