I think he is making a cloud clg. per NFPA because of the openings

*Glen Bue**low*

*Glen W. Buelow, Inc.*
*Fire Protection Design and Consulting216-469-7390** <330.665.4439>*


On Fri, Mar 22, 2024 at 1:26 PM Ed Kramer <[email protected]> wrote:

> In order to provide maintenance access to HVAC devices above a gyp
> ceiling, the project architect has proposed a rather clever solution.  I
> like it, but don’t know if the non-combustible space above the drop-in
> ceiling is required to be protected.
>
>
>
> To me, this seems to be more about openings in the ceiling and less about
> it being a cloud.  Full sprinkler protection will be provided beneath the
> gyp-board ceiling and the drop-in ceiling.
>
>
>
> NFPA 13 (2019) section 9.2.1.1.2 says I can have small openings in the
> ceiling and it appears the ceiling/openings meet the 2 conditions.  Is this
> section intended to apply to vertical openings?  I’ve assumed it was
> intended for horizontal openings, but it doesn’t specifically say that –
> though the wording in condition 2 seems to imply it.  A fire plume may not
> react the same to a vertical opening as it does to a horizontal opening.
>
>
>
> What do you guys/gals think?
>
> Ed
>
>
>
> [image: https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
>
>
>
>
>
>
>
> *Ed Kramer*
> *Design Manager *| *Bamford Fire Sprinkler Co., Inc.*
> P:    *913.432.6688*
> F:    *913.432.5294*
> M:   *785.766.4894*
> A:   *5134 Merriam Dr.  Shawnee Mission KS  66203*
>
>
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to