Where longitudinal bracing is provided for branch lines, the lateral bracing 
ZOI of grid mains does not have to include those lines per §9.3.5.9.6 (2016 
edition).

Steve L.

From: George Medina Jr. <[email protected]>
Sent: Thursday, March 21, 2024 2:55 PM
To: Discussion List On Issues Relating To Automatic Fire Sprinklers 
<[email protected]>
Subject: [Sprinklerforum] EQB and Zone Of Influence

I have a job where I have grid system where there is 6" grid mains and 2½" grid 
lines. In order to lessen the weight in the zone of influence of  the 6" grid 
mains I have included additional longitudinal bracing on the 2½" grid lines. Is 
it acceptable to exclude the Zone of Influence of the Longitudinally braced 2½" 
Grid lines from the Zone Of Influence of the 6" Grid Mains? Does NFPA-13 
address this scenario?


Thank You,
George Medina Jr.
Sr. Fire Sprinkler Designer
SINGLETON FIRE PROTECTION INC.
Office: (818) 252-5744
Cell: (323) 906-5701
Business Hours: 9:00am-5:00pm