Brian, You could use a non-ESFR sprinkler like the Tyco K17-231 standard response, standard coverage sprinkler. It comes in both upright and pendent. Area density method with a .60/2000. Then the rules for ESFR do not apply.
Anthony Carrizosa Project Manager | Fire Protection 7855 S 206th St Kent, WA 98032 Cell: 206-679-5283 | Office Dir: 253-341-4593 [cid:[email protected]] https://archerconstruction.com<https://linkprotect.cudasvc.com/url?a=https%3a%2f%2farcherconstruction.com%2f&c=E,1,Wdb65AWzMgSBzW3HDw91SfcRQCtxDUQKoJf-UowQ-WnB_WMosgG-8W7eLePJ42PwWQvLiQx16Pls052VqwHO7tKm-_u5AnWly0ewkNiMkxn-AjQb1JI,&typo=1> From: Brian Harris <[email protected]> Sent: Tuesday, March 19, 2024 5:10 AM To: [email protected] Subject: [Sprinklerforum] ESFR & Concrete Tee's I know there's been post about this topic but just wanted to bounce this off the group. We're installing a new system in an existing warehouse that has 22" deep concrete tee's, 48" stem to stem. The AHJ wants it designed for Group A plastics, rack/cartoned/expanded. I'm looking a NFPA-13 (2013) 17.2.3.1 using K17's @ 35psi. My thought is that ESFR heads will be required in every pocket per 8.12.4.1.6, 14.2.4.1, & 14.2.4.3. Am I on the right track? Thank you, Brian Harris, CET BVS Systems Inc. bvssystemsinc.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,vpwThwiiNOokaApVzNwM7PRBCVMVUQsAMfE88p0QJ2NODTvngvuiuxP3ZKWzS2K0GOtbuLytSXQeO-sXja600xK_yjWhwSQ4QgELVBVU&typo=1> Phone: 704.896.9989 Fax: 704.896.1935