Micah, 

 

I understand your project will be reviewed based on the language in the 2029 
edition of NFPA 13. However, section 1.5 Equivalency allows you to use 
alternate arrangements with technical documentation submitted to the AHJ.  What 
better way to show the level of safety is not being lowered, than to share the 
language from the next edition of the standard? 

 

Yes, the letter of the law is important, but so is the intent.  We know what we 
know when we know it and the arrangement of sprinklers or allowable modifiers 
in design applications that will exist in the next edition provide clarity and 
more so, in this case, a literal interpretation of this section, from the 
entire balloted committee.

 

I would encourage you to adopt Mr. Denhardt’s advice and share it with your 
AHJ. 

 

This is (of course) just my personal opinion and not intended to sound 
condescending in any way 

 

Best regards, 

 

Bob 

 

 

 


  <https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1> 


Bob Caputo, CFPS


President


American Fire Sprinkler Association

c:     760-908-7753


p:

214-349-5965 ext124 


w:

 <http://firesprinkler.org/> firesprinkler.org  


 <https://www.facebook.com/firesprinkler.org/>    
<https://twitter.com/afsa/status/1039528345367732224>    
<https://www.linkedin.com/company/american-fire-sprinkler-association-afsa-/>   
 <https://www.instagram.com/firesprinklerorg/> 

 

Treat Your Apprentices Like VIPs!

AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that comes 
straight from our expert instructors. They lead the way to ensure your men and 
women are trained, letting you focus on OJT. Click  
<https://www.firesprinkler.org/sprinkler-apprentice-training/> here to learn 
more and enroll

 

From: Micah Davis <[email protected]> 
Sent: Tuesday, March 19, 2024 7:09 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: EH 11k & High Temp RA reduction

 

Thank you, John.  That is MUCH clearer.  Unfortunately, the project in question 
is under the 2019 edition which leaves us with the uncertain language.  Your 
feedback helps me with my next steps, though.  


 

Thank you, 
Micah Davis 
(931) 242-1299

 

 

On Tue, Mar 19, 2024 at 12:40 AM John Denhardt <[email protected] 
<mailto:[email protected]> > wrote:

For the 2025 edition of NFPA 13, the proposed language is below:

 

Second Revision number 1084

 

19.2.3.2.7 Extra Hazard Occupancies.
19.2.3.2.7.1  
For extra hazard occupancies with ceilings not exceeding 30 ft (9.1 m) in 
height, the system area of sprinkler operation shall be permitted to be reduced 
by 25 percent without revising the density, but not to less than 2000 ft2 (185 
m2). where one of the following conditions occurs:
(1)  High-temperature sprinklers are used.
(2)  K-11.2 (160) or larger sprinklers are used.

19.2.3.2.7.2

The 25 percent reduction permitted by 19.2.3.2.7.1 shall only be permitted to 
applied once.

 

This language is pretty clear to me.  

 

The technical committee statement for this second revision is telling:

The current structure for the 25% reduction is unclear that the reduction can 
only be taken once with either high-temperature sprinklers or large orifice 
sprinklers. This revision makes the intent of the section clearer and will 
clarify the application of the requirements for multiple adjustments. Based on 
the fire testing data available at this time, the ceiling heights have been 
limited to 30 feet in height for taking the reduction.

 

 

While this language looks like it will make it into the 2025 edition of NFPA 
13, it still is subject to change until the Standards Council approves the 
release of this document around September 2024.

 




The above is my opinion and has not been processed as a formal interpretation 
in accordance with the NFPA Regulations Governing Committee Projects. This is 
provided with the understanding that the AFSA assumes no liability for this 
opinion or actions taken on it and they are not to be considered the official 
position of the AFSA, and/or NFPA or its technical committees.AFSA cannot 
provide design or consulting engineering services, and this opinion should 
therefore not be considered, nor relied upon, as such.

 

Thanks,

John

 





John August Denhardt, PE


Vice President, Engineering and Technical Services


American Fire Sprinkler Association


m: p:

301-343-1457
214-349-5965 ext 121


w:

 <http://firesprinkler.org/> firesprinkler.org  

        

 

 

Treat Your Apprentices Like VIPs!

AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that comes 
straight from our expert instructors. They lead the way to ensure your men and 
women are trained, letting you focus on OJT. Click  
<https://www.firesprinkler.org/sprinkler-apprentice-training/> here to learn 
more and enroll.

 

On Mon, Mar 18, 2024 at 3:16 PM John Denhardt <[email protected] 
<mailto:[email protected]> > wrote:

For this, high temperature or 11.2K is allowed, not both. 

 

I’m currently on a plane but I will quote you the reference later today. 

 

Either or, not both. 

 

John

John August Denhardt, P.E.

Vice-President Engineering and Technical Services

American Fire Sprinkler Association 

301-343-1457





On Mar 18, 2024, at 15:03, Mike Morey <[email protected] 
<mailto:[email protected]> > wrote:

 

I believe the intent was always that the K11.2 reduction was an alternative to 
high temp heads and not intended to allow both but it was never spelled out 
(other than that omission perhaps).  The revisions to the next edition are 
significant, but this item is consolidated into one that says you can take 25% 
reduction to no less than 2000 for one or the other.

 

Mike Morey

CFPS 3229 • NICET S.E.T. 123677

Project Manager • Fire Protection Group
Shambaugh & Son, LP an EMCOR Company

7614 Opportunity Drive • Fort Wayne, IN • 46825

direct 260.487.7824 /  cell 260.417.0625 /  fax 260.487.7991
email  <mailto:[email protected]> [email protected]

<image001.png>

 

From: Micah Davis <[email protected] <mailto:[email protected]> > 
Sent: Monday, March 18, 2024 2:51 PM
To: SprinklerForum <[email protected] 
<mailto:[email protected]> >
Subject: [Sprinklerforum] EH 11k & High Temp RA reduction

 

Hey everyone!  I need some help with the application of the remote area 
adjustment provisions in Chapter 19 (2019) of NFPA 13.   19. 3. 3. 2. 8 
addresses multiple adjustments but, interestingly, omits 19. 3. 3. 2. 7 in the 
list.   Should I interpret 

ZjQcmQRYFpfptBannerStart




This Message Is From an Untrusted Sender 


You have not previously corresponded with this sender. 

ZjQcmQRYFpfptBannerEnd

Hey everyone!  I need some help with the application of the remote area 
adjustment provisions in Chapter 19 (2019) of NFPA 13.  19.3.3.2.8 addresses 
multiple adjustments but, interestingly, omits 19.3.3.2.7 in the list.  Should 
I interpret this to mean that no other adjustments for EH design areas can be 
applied if the 11.2k or larger reduction is used?

 

Thank you,

Micah Davis

Ferguson Fire Design

931-242-1299

This message is for the named person's use only. It may contain confidential, 
proprietary or legally privileged information. No confidentiality or privilege 
is waived or lost by any mistransmission. If you receive this message in error, 
please immediately delete it and all copies of it from your system, destroy any 
hard copies of it and notify the sender. You must not, directly or indirectly, 
use, disclose, distribute, print, or copy any part of this message if you are 
not the intended recipient.


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected] 
<mailto:[email protected]> 


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected] 
<mailto:[email protected]> 

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to