Personally I would stick to LxW spacing and not sweat measuring along the
circumference especially since thirteen sprinklers seems like overkill for
the roughly 1256 sq ft of area. You could look to 8.6.3.2.5 (2016) for
something along the same lines but this section is for measuring max
distance from curved walls but the idea is the same: the standard has you
measuring straight out and not along the circumference. By my estimation
you could probably get by with only 8 sprinklers (with a 20 ft throw), one
at each quadrant and in-between quadrants, so I wouldn't lose sleep with
thirteen EC sprinklers in this area.

AJ

<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail>
Virus-free.www.avg.com
<http://www.avg.com/email-signature?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail>
<#DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2>

On Fri, Mar 8, 2024 at 2:58 PM Fpdcdesign <[email protected]> wrote:

> I have already flexed my PE muscle and made the radical suggestion that
> they use concealed pendants instead of extended sidewalls. I’m not sure
> they will go for it because an intelligent solution would be inconsistent
> with the rest of the building.
>
>
>
> On Mar 8, 2024 at 3:41 PM, <Ron Greenman <[email protected]>> wrote:
>
> I'm thinking this may be one of those occasions where that PE after your
> name may need to be summoned, Todd.
>
> On Fri, Mar 8, 2024 at 11:22 AM Fpdcdesign <[email protected]> wrote:
>
>> Light Hazard. Waiting room
>>
>>
>>
>> On Mar 8, 2024 at 2:18 PM, <Rick Matsuda <[email protected]>> wrote:
>>
>> What’s the occupancy of the space?
>> Rick Matsuda
>>
>> On Mar 8, 2024, at 1:13 PM, Fpdcdesign <[email protected]> wrote:
>>
>> 
>> I am working on a project that has a 40 ft diameter circular ceiling at
>> an elevation of 10 ft that is surrounded by an 8 ft ceiling. The existing
>> protection to the high areis provided by 18 extended coverage sidewall
>> sprinklers around the perimeter. They are renovating the space and want us
>> to install new protection using 13 extended coverage sidewall sprinklers.
>> My question is how do you space them along the wall? Everything I have seen
>> in 13 and manufacturer’s literature details spacing on straight walls.
>>
>> The circumference of the space is about 125 ft and 13 sprinklers would be
>> spaced at about 9.5 ft, but angled towards each other. Is this going to
>> present a problem? Who else has dealt with this?
>>
>> Todd G Williams, PE
>> Fire Protection Design/Consulting
>> Stonington, CT
>> 860-535-2080 (ofc)
>> 860-554-7054  (fax)
>> 860-608-4559 (cell)
>>
>> _________________________________________________________
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> [email protected]
>>
>> _________________________________________________________ SprinklerForum
>> mailing list:
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> [email protected]
>>
>>
>> _________________________________________________________
>> SprinklerForum mailing list:
>>
>> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
>> To unsubscribe send an email to
>> [email protected]
>
> _________________________________________________________ SprinklerForum
> mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
>
>
> _________________________________________________________
> SprinklerForum mailing list:
> https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
> To unsubscribe send an email to
> [email protected]
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to