If you have a combination standpipe, you may need to be cognizant of exceeding 
system component rating. 2019 edition of NFPA 14 has an added requirement:

7.8.1.2.1
The pressure required at the fire department connection for manual standpipes 
shall not exceed the working pressure of the system components of the standpipe 
system or sprinkler system when the system is a combined system.




Travis Mack, SET
M.E.P.CAD | Instructor / Support
181 N. Arroyo Grande Blvd. #105 I Henderson, NV 89074
www.mepcad.com<http://www.mepcad.com/> | m: 480.547.9348| Whatspp: +14805479348
Email: [email protected]

AutoSPRINK  |  AutoSPRINK FAB  |  AutoSPRINK RVT  |  AlarmCAD

From: Kevin Hall <[email protected]>
Sent: Friday, February 9, 2024 10:15 AM
To: George Medina Jr. <[email protected]>; Discussion list on issues 
relating to automatic fire sprinklers <[email protected]>
Subject: [Sprinklerforum] Re: STANDPIPE PSI SIGNAGE

178

[https://www.dropbox.com/s/g4h8r7hdtsr6154/AFSA_L.png?raw=1]
Kevin Hall, M.Eng., P.E., ET, CWBSP, PMSFPE
Sr. Manager, Engineering and Technical Services
American Fire Sprinkler Association
p:
214-349-5971
w:
firesprinkler.org<http://firesprinkler.org/>

Treat Your Apprentices Like VIPs!
AFSA’s Virtual Instruction Program (VIP) for Apprentices is training that comes 
straight from our expert instructors. They lead the way to ensure your men and 
women are trained, letting you focus on OJT. Click 
here<https://www.firesprinkler.org/sprinkler-apprentice-training/> to learn 
more and enroll.


On Fri, Feb 9, 2024 at 12:14 PM George Medina Jr. 
<[email protected]<mailto:[email protected]>> wrote:
If the required pressure at the FDC is 178 psi and the City pressure is  84 
psi, do I subtract the 84 psi from the 178? or do I just put the 178 psi on 
sign?

George Medina Jr.
Sr. Fire Sprinkler Designer
SINGLETON FIRE PROTECTION INC.


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to