Steel piping should not be an issue.  There may be some concern with
plastic piping.

Here is the general requirement from the 2021 IMC.  No specific prohibition
on plastic piping I could locate, assuming it meets the flame spread
requirements.

*602.2.1 Materials within plenums. Except as required by Sections 602.2.1.1
through 602.2.1.8, materials within plenums shall be noncombustible or
shall be listed andlabeled as having a flame spread index of not more than
25 and a smoke-developed index of not more than 50 when tested in
accordance with ASTM E84 or UL 723.*

Mike Slaughter
Risk Reduction Division
Travis County Emergency Services District 2
Office:    (512) 989-4531
[email protected]





On Mon, Feb 5, 2024 at 3:56 PM Brian Harris <[email protected]>
wrote:

> Is there anywhere in code that says sprinkler pipe is not allowed in a
> space above a ceiling being used as a return air plenum? I know we’ve done
> it before but now have a superintendent telling us it’s not allowed on his
> job….. Drawings were approved, centerlines clearly called out. Nothing on
> the contract drawings saying the space is off limits, etc.
>
>
>
> Thank you,
>
>
>
> *Brian Harris, CET*
>
> BVS Systems Inc.
>
> bvssystemsinc.com
> <https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fbvssystemsinc.com%2f&c=E,1,Jogx9LlwOLpPQ2VYAh4Ww4VH4X3tQmQpB4TEtnev2Y4zVz3oeLSe-T1CFZgeK_kPHTn0ids6glFDyDaRQsxoTnzob8VSxMi2yAsucAP8&typo=1>
>
> Phone: 704.896.9989
>
> Fax: 704.896.1935
>
>
>
> _________________________________________________________
> SprinklerForum mailing list:
>
> https://linkprotect.cudasvc.com/url?a=https%3a%2f%2flists.firesprinkler.org%2flist%2fsprinklerforum.lists.firesprinkler.org&c=E,1,_5ViUrcxAxpHhDVkRI2q1KkK2dbR__m2T3IiIatKP8xihgV9Uj1x_YbhoHB6wpzc8McnVYDcextBFKMLPZmrIOlTx3y4-yRU2bDJbsSu&typo=1
> To unsubscribe send an email to
> [email protected]
>
_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to