I hope I am reading this wrong but here goes. We are using NFPA #13 (2022ed) 
section 23.4.

We have a client that said they would be storing exposed expanded group A 
plastics on racking and we advised about the requirement for vertical barriers.

They now supply us with the racking drawing and they have multi-row racking, I 
had assumed the same requirement for the vertical barriers, but the more I read 
the more confused I have become.

Section 23.4 Protection of Exposed Expanded Group A Plastics.
23.4.1 Protection on single, double and multi-row racking
23.4.7 Racks shall have vertical barriers spaced at not more than 16'-6"
23.4.7.2 The plan area of storage between the vertical barriers and aisles 
shall not exceed 124ft²

So if my math is correct and they install a vertical barrier at every second 
upright (16'6") apart this would mean that the maximum rack depth would be 
7'-6".

124/16.5=7.5

This is barely double row racks with a flue space and would never be able to 
protect multi-row racking.

I guess my question is have I missed something or is this correct?

Thank You

James Crawford
Phaser Fire Protection Ltd.
Phone 604-888-0318
Cel: 604-790-0938
Email [email protected]<mailto:[email protected]>
Web: www.phaserfire.ca<http://www.phaserfire.ca>