Can I apply the above Section to the following scenario:

I have an area which requires .60 over 2,000 sq. ft.. In the area requiring 
.60, there are only 11 heads in the room and I am calcing 7 heads on the grid 
line (1 grid line supply the room) at 115 sq. ft. per head. In order to calc 
2,000 sq. ft. I am having to extend my calc into an area which requires only 
.425 over 2,000 sq. ft. (and 135 sq. ft. per head). I am using Tyco EC-25 
through out. In the Higher density Calculation, can I apply the specific head 
requirements from the lesser density calc area? (.425 over 135 sq. ft.) into my 
calculation? The 2 areas are separated by 1 hour rated walls. 
Thanks for any Input,George Medina Jr.