“assuming there’s a 460/3 ph in the pump room.”
Steve L.

That is what I am wondering. If they have the wrong step-down in there and are 
looking for alternate ways to save $%$$.

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Manager – Southwest Region
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
3508 Hwy. 557
West Monroe, LA. 71292
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<http://www.fergusonfire.com/>


From: Steve Leyton <[email protected]>
Sent: Friday, January 19, 2024 5:25 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Re: Phase Converter

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
You’re right, the JP cannot be supplied from or downstream of the controller, I 
didn’t mean to imply you can as that’s all spelled out in Article 695.3.  But 
you can definitely supply it with the same dedicated circuit as the main pump 
if you tap ahead of the controller.   The question on the table is whether a 
separate circuit of a different current is appropriate or necessary since Brian 
included a JP rated for the same current as the FP.   So the electrician’s 
response that he “can’t” provide a conforming power supply that matches the JP 
is gibberish, assuming there’s a 460/3 ph in the pump room.

Steve L.


From: AKS-Gmail-IMAP <[email protected]<mailto:[email protected]>>
Sent: Friday, January 19, 2024 2:18 PM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Phase Converter

The way I understood it, the NEC does not permit using the fire pump control 
panel as a junction box. Any tap to the electrical power conductors leading 
into the fire pump control panel used for powering the jockey pump is using the 
control panel as a junction box.

On Jan 19, 2024, at 11:42 AM, Steve Leyton 
<[email protected]<mailto:[email protected]>> wrote:

This industry can be a roller coaster of challenges and rewards, and also 
brings those occasional scenarios that can (perhaps should) render you 
speechless.   For me, some of the most entertaining moments have been when 
someone stridently insists that we “can’t” do something that’s been a common, 
even standard practice for years…

Steve L.

From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Friday, January 19, 2024 5:06 AM
To: Discussion list on issues relating to automatic fire sprinklers 
<[email protected]<mailto:[email protected]>>
Subject: [Sprinklerforum] Re: Phase Converter

Matt-
We’ve asked that same question and the electrician insist he can’t do that.

Thank you,

Brian Harris, CET
BVS Systems Inc.

From: [email protected]<mailto:[email protected]> 
<[email protected]<mailto:[email protected]>>
Sent: Friday, January 19, 2024 8:03 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Re: Phase Converter

Can they not just piggy-back from the Main Fire Pump panel?

I had always thought with the Fire Pump power being SUSE rated, that that is 
what they have always done.
Hence the reason the Jockey Pump ratings always matched the Fire Pumps.

R/
Matt

Please rate our customer 
service<https://survey.medallia.com/?emailsignature&fc=3539&bg=Fire%20and%20Fabrication>

Matthew J. Willis, CWBSP, CET
Engineering Manager – Southwest Region
FERGUSON FIRE DESIGN, LLC
A Wholly Owned Subsidiary of Ferguson Fire & Fabrication, LLC
3508 Hwy. 557
West Monroe, LA. 71292
C: 307-236-8249
[email protected]<mailto:[email protected]>
www.FergusonFire.com<http://www.fergusonfire.com/>


From: Brian Harris <[email protected]<mailto:[email protected]>>
Sent: Friday, January 19, 2024 6:59 AM
To: 
[email protected]<mailto:[email protected]>
Subject: [Sprinklerforum] Phase Converter

Caution:  This email originated from outside of the organization.  DO NOT click 
links or open attachments unless you recognize and trust the sender.
________________________________
We have a job with a fire pump. Electrician ran 3-phase/460v for the main pump 
but not for the jockey pump. They’re asking if using a phase converter is an 
option instead of ordering a single-phase jockey pump. Anyone have experience 
with this?

Thank you,

Brian Harris, CET
BVS Systems Inc.
bvssystemsinc.com<http://bvssystemsinc.com/>
Phone: 704.896.9989
Fax: 704.896.1935


_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org<https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org>
To unsubscribe send an email to 
[email protected]<mailto:[email protected]>

_________________________________________________________
SprinklerForum mailing list:
https://lists.firesprinkler.org/list/sprinklerforum.lists.firesprinkler.org
To unsubscribe send an email to [email protected]

Reply via email to