I believe that two layers of the Type X make the space between the presumably 
non-combustible ceiling and the sheetrock a non-combustible concealed space.


Steve Leyton

(Sent from my smartphone; please excuse typos and voice-to-text corruptions.)



-------- Original message --------
From: "George Medina Jr." <[email protected]>
Date: 1/16/24 10:12 AM (GMT-08:00)
To: Discussion List On Issues Relating To Automatic Fire Sprinklers 
<[email protected]>
Subject: [Sprinklerforum] Concealed Spaces Not Requiring Sprinkler Protection

There is a one hour floor assembly which consist of 22" Red-S joist (Wood 
Chords with Tube Bars) with 2 layers of type x gypsum board on channels below 
joist. Could it be considered limited combustible construction inside the bar 
joist? Or am I just grasping for straws, and it needs sprinklers.

Thanks For any replies,

George Medina Jr.